SJD ~ Mentor Arms Jun 6, 2013 #1 Went to look at a consumer unit this evening, the owner is having trouble with the RCD not working, notice anything odd about the installation? Attachments 2013-06-06-331-sharp.jpg 476.9 KB · Views: 137
Went to look at a consumer unit this evening, the owner is having trouble with the RCD not working, notice anything odd about the installation?
telectrix ~ Mentor Arms Jun 6, 2013 #5 busbar gives it away. all breakers are fed direct from main switch and looks like RCD L on both in and out is connected direcly to main switch Lout. .
busbar gives it away. all breakers are fed direct from main switch and looks like RCD L on both in and out is connected direcly to main switch Lout. .
telectrix ~ Mentor Arms Jun 6, 2013 #6 obviously B&Q need to update the you can do it manual. or is that what you get when you accept the lowest quote?
obviously B&Q need to update the you can do it manual. or is that what you get when you accept the lowest quote?
SJD ~ Mentor Arms Jun 6, 2013 #8 Yes, RCD L in and out are indeed both connected to main switch L out. The owner has already had 2 electricians visit, one said the CU needed a new RCD fitting, other other said it needed completely rewiring ...
Yes, RCD L in and out are indeed both connected to main switch L out. The owner has already had 2 electricians visit, one said the CU needed a new RCD fitting, other other said it needed completely rewiring ...
P Phoenix Jun 6, 2013 #9 I'm impressed! I'm obviously not as stupid as I thought!!!! It beggars belief, it really does...
S stuartcourt Jun 6, 2013 #10 SJD said: Yes, RCD L in and out are indeed both connected to main switch L out. The owner has already had 2 electricians visit, one said the CU needed a new RCD fitting, other other said it needed completely rewiring ... Click to expand... 2 muppets you mean
SJD said: Yes, RCD L in and out are indeed both connected to main switch L out. The owner has already had 2 electricians visit, one said the CU needed a new RCD fitting, other other said it needed completely rewiring ... Click to expand... 2 muppets you mean
E Engineer54 Jun 7, 2013 #12 stuartcourt said: 2 muppets you mean Click to expand... Correct, ...but what else would you expect from electrical trainee's?? It looks as if this CU installation has had 3 of the buggers, one being the installer!! lol!!
stuartcourt said: 2 muppets you mean Click to expand... Correct, ...but what else would you expect from electrical trainee's?? It looks as if this CU installation has had 3 of the buggers, one being the installer!! lol!!
telectrix ~ Mentor Arms Jun 7, 2013 #13 yep, first miss piggy, followed by statler and waldorf. or was it curly, larry and mo.