Went to look at a consumer unit this evening, the owner is having trouble with the RCD not working, notice anything odd about the installation?
 

Attachments

  • 2013-06-06-331-sharp.jpg
    2013-06-06-331-sharp.jpg
    476.9 KB · Views: 137
busbar gives it away. all breakers are fed direct from main switch and looks like RCD L on both in and out is connected direcly to main switch Lout. .
 
obviously B&Q need to update the you can do it manual. or is that what you get when you accept the lowest quote?
 
Yes, RCD L in and out are indeed both connected to main switch L out.

The owner has already had 2 electricians visit, one said the CU needed a new RCD fitting, other other said it needed completely rewiring ...
 
I'm impressed! I'm obviously not as stupid as I thought!!!! It beggars belief, it really does...
 
Yes, RCD L in and out are indeed both connected to main switch L out.

The owner has already had 2 electricians visit, one said the CU needed a new RCD fitting, other other said it needed completely rewiring ...
2 muppets you mean
 
yep, first miss piggy, followed by statler and waldorf. or was it curly, larry and mo.
 