Discuss Cupboard under stairs lighting in the UK Electrical Forum area at ElectriciansForums.net

B

Brns

Hi

I'm looking to fit a light in the cupboard under my stairs, there is a single socket on the wall next to the cupboard door in the hallway with the wires clipped on the inside.
Not certain yet if this is a spur or on the normal ring circuit but if it's a spur then could I possibly fit a 13a fcu (switched) then wire some 1.5mm cable to a ceiling rose for the light, switched fcu acting as the main switch for the light?
 
you can do that, but fit a 3A or a 5A fuse in the FCU.
 
Hi

I'm looking to fit a light in the cupboard under my stairs, there is a single socket on the wall next to the cupboard door in the hallway with the wires clipped on the inside.
Not certain yet if this is a spur or on the normal ring circuit but if it's a spur then could I possibly fit a 13a fcu (switched) then wire some 1.5mm cable to a ceiling rose for the light, switched fcu acting as the main switch for the light?
It could be a Spur from the RFC
 
Either way he could still spur for a light.
Yes I know, but reading the thread it seemed to me that the OP, maybe had some difficulty distinguishing the difference between a Radial and a spur, no disrespect to the OP either.
 
If the existing socket is spurred from the ring final and although it is not likely to overload you shouldn't add another point to it. They would both require protection.
 
It's on the ground floor rfc as there is only one mcb for ground sockets and there are two 2.5mm cables, 1 coming from ccu to the socket and the other from socket going up into ceiling to the next socket, also I checked with my multimeter, turned the power off & checking it was off, then proceeded to check between each live, neautral & earth conductor at socket & ccu to get continuity so it being just a socket on the rfc, I will fit a 3-5amp switched fcu to be on safe side then wire from the in 1.5mm to the light, yes or no?
 
It's on the ground floor rfc as there is only one mcb for ground sockets and there are two 2.5mm cables, 1 coming from ccu to the socket and the other from socket going up into ceiling to the next socket, also I checked with my multimeter, turned the power off & checking it was off, then proceeded to check between each live, neautral & earth conductor at socket & ccu to get continuity so it being just a socket on the rfc, I will fit a 3-5amp switched fcu to be on safe side then wire from the in 1.5mm to the light, yes or no?
Brns, what you are saying does not prove this socket is indeed part of a RFC, it more than likely is but to prove that it is you need to carry out tests,as you are training, have you not been instructed on Safe isolation, a multi meter is not the correct instrument to use.
 
Brns, what you are saying does not prove this socket is indeed part of a RFC, it more than likely is but to prove that it is you need to carry out tests,as you are training, have you not been instructed on Safe isolation, a multi meter is not the correct instrument to use.
I'll try posting the vids again

 
sounds like he is testing at the consumer unit and at the socket using the low resistance ohm setting on his multi meter. what else would you have him do to prove it's a ring?

sounds like he is testing at the consumer unit and at the socket using the low resistance ohm setting on his multi meter. what else would you have him do to prove it's a ring?
sounds like he is testing at the consumer unit and at the socket using the low resistance ohm setting on his multi meter. what else would you have him do to prove it's a ring?
Do it the right way, qualified people in whatever sphere of work they are involved in have a moral obligation to help trainees, inexperienced people, in the correct procedures, I believe I have done that, in posting 2 videos on the correct procedures, if you don't agree then that's down to you, as a qualified Electrician.:)
 
Last edited:
Yes, I do know how to do safe isolation, yes I do know how to do a ring final circuit test with the figure off 8 connection between live & neautral but I'm sorry for not writing down every little detail step by step of what I'm doing, I've got much better things to do that's why all I wanted was a simple answer & I'm sorry my mistake not a multimeter I meant a Kewtech KT63 multifunction tester and next time I will put every detail step by step off it all & even let you know what I'm having for dinner if you like
 
Yes, I do know how to do safe isolation, yes I do know how to do a ring final circuit test with the figure off 8 connection between live & neautral but I'm sorry for not writing down every little detail step by step of what I'm doing, I've got much better things to do that's why all I wanted was a simple answer & I'm sorry my mistake not a multimeter I meant a Kewtech KT63 multifunction tester and next time I will put every detail step by step off it all & even let you know what I'm having for dinner if you like
A multi function tester is not the correct instrument to use for safe isolation either. To quote a Canadian TV construction personality "if you are going to do it, do it right the first time" gets my vote every time, no short cuts in Electrikery.o_O
 
A multi function tester is not the correct instrument to use for safe isolation either.
Your going off the subject now as I know how & what to do with safe isolation but like I said I'm not here to write every bit of detail of what I've done, I've done the isolation (SAFELY AND CORRECTLY) I've done the ring final circuit test (SAFELY AND CORRECTLY) so now what would be the correct way off fitting a light then? fitting a 3-5amp switched fcu then feeding from that to a ceiling rose using 1.5mm cable or do you want me to say 1.5mm twin and earth cable
 
Your going off the subject now as I know how & what to do with safe isolation but like I said I'm not here to write every bit of detail of what I've done, I've done the isolation (SAFELY AND CORRECTLY) I've done the ring final circuit test (SAFELY AND CORRECTLY) so now what would be the correct way off fitting a light then? fitting a 3-5amp switched fcu then feeding from that to a ceiling rose using 1.5mm cable or do you want me to say 1.5mm twin and earth cable
Well OK then
 
Yes, I do know how to do safe isolation, yes I do know how to do a ring final circuit test with the figure off 8 connection between live & neautral but I'm sorry for not writing down every little detail step by step of what I'm doing, I've got much better things to do that's why all I wanted was a simple answer & I'm sorry my mistake not a multimeter I meant a Kewtech KT63 multifunction tester and next time I will put every detail step by step off it all & even let you know what I'm having for dinner if you like

Easy Tiger. Don't think anyone will be predisposed to help, if you lose your temper :(
 
Oh dear, you started off so well but then started showing the attitude. You will find you don't get much assistance if you deal with things in this manner. Chill out - you seem to make out you know everything but then have a very basic query, which is why people probably assumed your lack of knowledge and ability. Daz
 

Reply to Cupboard under stairs lighting in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Wanting to add 2 strips of led lights down each side of underneath of the stairs, I have a socket I can spur off, into a fused switch, been...
Replies
1
Views
817
This could possible have been a poll, but really just opening up for suggestions and feedback on where folks think an isolation switch for an...
Replies
12
Views
3K
I'll start by saying - I have absolutely no intention of doing any wiring or anything electrical myself. You get someone professional to do a...
Replies
8
Views
821
Hey, I lifted a few sockets from a wall so I could paint without having to cut in around them. I haven’t lifted any light switches yet. When...
Replies
4
Views
926
Morning All I recently completed my first re wire and board change, (with help from the owner who is a gas fitter and plumper, who works with my...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock