Discuss Curve (Denmans) RCDs in the Electrical Tools and Products area at ElectriciansForums.net
Anyone had problems with these rcds? Control Gear Direct, 30mA, 63A 2 pole..
I recently bought two 10-way dual rcd boards from denmans.. first one had an rcd which didnt trip on test button, even with load removed. Second rcd didnt trip under 300mS, but button worked.
Swapped them for the rcds in the second board I had (lucky me, I thought).. one rcd was ok but second one also had trip time problem. swapped the rcds around and the problem followed the rcds.
Got denmans to hotfoot replacement two boards that day... one rcd no trip on test button, the other had trip time problem!
The rcd which "worked" ok, I subsequently found to be a bit intermittent also on trip time. Once i put it on x2 test it seemed to settle down. but also the test button sometimes takes a while to trip as well! ie had to hold it down for a second or two.. the test results when working show no unusual results, all appliances were disconnected.
I did wonder if my tester (metrel 31000) was beginning to play up but worked ok at home and was only calibrated a few weeks ago.
I also put in the only other rcd i had with me, a Hager, and this has been fine.
Control Gear have posted to me 4 replacement rcds with test results, so ill see what happens..
First time ive had NO Trip problems, usually the other way...
I’ve been to 3 jobs in past 7 days, with a total of 7 RCDs, 4 in 1, 1 in another, and 2 in the job today.
All 7 wouldn’t time out. Phoned my rep and he said that’s why his place don’t sell them as they wouldn’t time out, that’s the way they came from factory, every one of them.
Anyone else found this?
I would agree with Lee above, test the RCD at the terminals with no load connected.
(Eaton RCBOs need to be tested from the cable entry rather than the terminals as the sensing coil is above the terminal.)
I have used some Lewden, curve, Denmans, CGD RCDs but I have not yet had a problem with them. They are bottom of the price range but they should operate OK.
Having seven fail at one installation sounds on the edge of possibility.
Reply to Curve (Denmans) RCDs in the Electrical Tools and Products area at ElectriciansForums.net
I sorted the fault fairly quickly as it happens but only because I'd come across it once before and at the time a few people said it couldn't...
Hi all, There's 2 single fan ovens in the house my mother recently moved into. Posh elecronic AEG units. It's been sat empty for a year, so the...
What should you do if a client has a CU that is a split board protected by 2 * 63Amp 30mA double pole RCCDs, you took Zs and tested both RCCDs by...
My circuit panel has two banks of breakers, each bank protected by an RCD. One of these RCDs has been problematic in that it trips intermitantly...