The other day I found some DC lurking where it did not ought to be. The new sticker that indicated it had passed an electrical safety test was a ruse, and the lamp at the bank of sockets was glowing a lovely bright red, indicating these were all on and you could satisfy your longing for AC here. There was no AC, but there was 130V DC, more than enough for a nasty belt. To put you in the picture, this was in an outside broadcast vehicle, and the stray voltage was coming from a fault with the onboard UPS.

This led me to thinking, because in the last month or so, I have come across some stray, very low, DC voltages in what should be dead domestic circuits. I'm assuming that they were leaking out of a smoke alarm or discharging laptop or similar. But here's the thing, do you test for DC when you test for dead? I'm beginning to wonder if I should be.
 
I only test for DC if there's a remote chance it might be present. For example if I was working on an installation that had a DC solar array connected I might include a DC test if I was testing for isolation...but probably not. I've never heard of a UPS being able to inject DC back into its power supply, did you discover what caused this? Can't help thinking it might have been just a surface voltage that was picked up by a super-sensitive digital tester with a very high input impedance.
 
Is the UPS connected with an inverter or does the vehicle have equipment that operates on DC anyway? I presume it has another main means of power normally too?

Bit of an obscure one!
 
The other day I found some DC lurking where it did not ought to be. The new sticker that indicated it had passed an electrical safety test was a ruse, and the lamp at the bank of sockets was glowing a lovely bright red, indicating these were all on and you could satisfy your longing for AC here. There was no AC, but there was 130V DC, more than enough for a nasty belt. To put you in the picture, this was in an outside broadcast vehicle, and the stray voltage was coming from a fault with the onboard UPS.

This led me to thinking, because in the last month or so, I have come across some stray, very low, DC voltages in what should be dead domestic circuits. I'm assuming that they were leaking out of a smoke alarm or discharging laptop or similar. But here's the thing, do you test for DC when you test for dead? I'm beginning to wonder if I should be.

I cannot see how a UPS that meets current safety standard could actually output 130V DC so i think you have a red herring here.

It's more likely the engineer have broadcast equipment that operates at 130V DC (I know a lot does) and they have used sockets as convenient ways to output this DC... Grant you it's blinking dangerous because 130V DC is lethal and excellent for welding!!
 
@Outspoken, quite the point and well made. @1ManRiot It is normally powered from a Film & TV genny on a single phase 32A.

The UPS was faulty, is the answer, and a more potentially dangerous fault I have yet to discover. Were it not for the little neon, any socket'n see, or wand or whatever would have given the impression that all was safe and I think this is just another case that validates the use of probes. The "engineer" that "safety tested" that particular bank of sockets has been dealt with.
 