If you have a copy of BS7671 regs your answer is on pages 46 to 50 if not waht system do you have ie TT TNCS TNS and do you have fuses or RCD/MCBs

Chris

Normally 0.4 seconds for domestic circuits and 5 seconds for distribution if I remember correctly

Chris
 
Last edited by a moderator:
As above, but the 5s disconnection time depends on the installation method of the distribution circuit.

Also, TT systems disconnection times are lower.
 
and because of that, osg says generally to achieve the disconnection times, EVERY circuit must be protected by an RCD, in one form or another...on a TT system
 

Reply to disconnection time permitted for protective devices? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock