Have a look at Table 41.1 and then have a read of regs 411.3.2.2 through to 411.3.2.6
 
Ok lets not get bogged down with this, maybe i am thinking about it too deeply.
If i have a distribution circuit then the disconnection time is five seconds. Are the circuits supplied from this distribution circuit then classed as a final circuits and then subject to the 0.4 second disconnection time provided they are protected by a device of 32 amps or less.
 
And if it is a TT system ?

Have a read of the sections I said and see what you think.
 
Right well I'm having arguments at work with a fellow' tester'Basically its an old installation 40+ all bs88 fuses, its a tn system so 32 and under should be 0.4 is my view however he argues there all 5s because a bs88 fuse cannot achieve a 0.4 disconnection time without the installation being protected by a trip, can't find much in the regs because the install is so old
 
Last edited:
Well according to appendix 3 they expect a BS 88-2.2 and an 88-6 to trip out in anything from 0.1 to 5 secs, and I don't think that as changed much throughout the years.

What is a trip?? an MCB ??
 
Right well I'm having arguments at work with a fellow' tester'Basically its an old installation 40+ all bs88 fuses, its a tn system so 32 and under should be 0.4 is my view however he argues there all 5s because a bs88 fuse cannot achieve a 0.4 disconnection time without the installation being protected by a trip, can't find much in the regs because the install is so old

Of course they can achieve 0.4s if the fault current is high enough. Have a look at Table 41.2 BRB for Max Zs values for 0.4s.

Basically...

TN system

Final circuits ≤ 32A = 0.4 seconds
Final circuits > 32A and distribution circuits = 5 seconds

TT system

Final circuits ≤ 32A = 0.2 seconds
Final circuits > 32A and distribution circuits = 1 second
 
Right well I'm having arguments at work with a fellow' tester'Basically its an old installation 40+ all bs88 fuses, its a tn system so 32 and under should be 0.4 is my view however he argues there all 5s because a bs88 fuse cannot achieve a 0.4 disconnection time without the installation being protected by a trip, can't find much in the regs because the install is so old

As fellow 'testers' I'm a bit concerned that neither of you could access the facts without the help of a forum?

It's pretty basic stuff....
 
Yes well my copy of bs7671 wasn't available to show him the regs, iv only got into testing full time recently and the other tester has been doing it for 30+ years and wouldn't belive me. I have quite a few doubts about him but hes been the main/only tester the company I work has ever had and does not take kindly to me questioning him. But thanks for you knowlegable responses
 
It was the bit where you said 'can't find much in the reg's...'

What has the age of the installation got to do with the disconnection time of a fuse to BS 88?
 
Last edited:
Well when i told him about tn systems having a 0.4 32amp and under and 5sec diconnection time his arguement was that because the installation was so old that he would test it to the 15th edition of the regs, like i said im not going to argue because I will not win. I am used to doing eic reports with other firms I have worked with not pir's. I only gained my 2391-10 in May of this year and im only 24 so I hoping to learn aswell but as I said he's set in his ways and will not back down
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

diditrain

Arms
-
Joined
Location
north west
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
Disconnection times
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
16

Advert

Thread statistics

Created
diditrain,
Last reply from
adslev,
Replies
16
Views
11,442

Advert

Back
Top