Reading the on-site guide it’s states for socket outlets appendix A table A2 row 9 that 32A ring sockets in an office it can be 100% of the largest circuit and then 50% of the remaining circuits.

However I have came across a calculation were the original designer has assumed that they know what will be used on the sockets ( pc’s) in this case and has calculated diversified current based on this.

Has anyone else came across this before ? I am thinking g this is not in line with the guide.

Thanks
 
but the guide was written when computers had valves inside.
 
i've never designed a "wise" how do you do it?:D:D:D:D.
 

Reply to Diversity allowance on sockets based on OSG in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock