Hi,
Reading the on-site guide it’s states for socket outlets appendix A table A2 row 9 that 32A ring sockets in an office it can be 100% of the largest circuit and then 50% of the remaining circuits.
However I have came across a calculation were the original designer has assumed that they know what will be used on the sockets ( pc’s) in this case and has calculated diversified current based on this.
Has anyone else came across this before ? I am thinking g this is not in line with the guide.