Hi guys,

QUESTION: Do you test the suppliers earth conductor for continuity???

The guidance note 3 2.6.5 refers to regulation 643.2.11 which requires a continuity check be carried out on all protective conductors including: EARTHING CONDUCTOR, CPC's and bonding conductors. I am aware of the bonding conductors and CPC's being tested. But the earthing conductor to be tested? Does this mean that when I have carried out safe isolation, I am supposed to remove the main earthing conductor (from the supplier) from the MET (to remove parallel paths) and carry out a continuity test of this short piece of suppliers earth?

I am currently writing my NVQ inspection and testing unit. I have completed my AM2, and testing units and never come across this test for initial verification, I don't think I've seen it done on any youtube revision videos too.

It would make sense to test it though right? As I was taught you carry out the sequence of test in the order it is in, because the next test always depends on the previous test if that makes sense lol? There would be no point in testing the bonding conductor/ CPC's if there is no suppliers earth right?

Thanks in advance for anyone who can help out!
 
Test the Ze of the incoming earth whilst disconnected from the installation. A live test.
Continuity testing of bonding and cpc's is required, even if there is a problem with the incomer.....for when it is reinstated.
 
  • Like
Reactions: pc1966

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

ppelec100

Arms
~
Joined
Location
London
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Trainee Electrician

Thread Information

Title
Do you test the suppliers earth conductor for continuity??? (Initial verification)
Prefix
N/A
Forum
Electrical Testing & PAT Testing Forum
Start date
Last reply date
Replies
2

Advert

Thread statistics

Created
ppelec100,
Last reply from
davesparks,
Replies
2
Views
2,256

Advert