Did you IR test the lighting?
No borrowed neutral all lighting is segregated to individual circuits Everything works fine other than under unit lights
it's possible that the L feed to these under cupboard lights comes from another circuit. rather a borrowed L than a borrowed N.
Tel that's post stealing at its finest :30:
it's possible that the L feed to these under cupboard lights comes from another circuit. rather a borrowed L than a borrowed N.
Where are the under unit lights switched from? I had a similar problem once . They picked the live from the kitchen switch and a neutral from a kitchen socket.
This maybe true mate mate link from main kitchen common to under hint commonit's possible that the L feed to these under cupboard lights comes from another circuit. rather a borrowed L than a borrowed N.
Sounds good to me mate I will check and test tomorrow mate appreciate guysTenner says its a borrowed neutral , you say that there is a link at the 2 gang kitchen switch , as already mentioned the neutral has got to be from another circuit fed from the other RCD, most likely the kitchen sockets .
This is exactly the reason why pre-testing is so important and should be as important a job as making sure the kettle is boiled before you kill the power. test test and test again

And a pan full of water on the hob..... just in case![]()