i'm currently running a commercial site of a new gym. We have installed lighting trunking with thorn pop packs direct onto the trunking.
When testing continuity at any db's my tester is flashing up a voltage of 009v when testing to earth (was testing a ring r1+r2). All circuits have been mega'ed and are clear and all bonding is in place. When the mccb is turned off to two of the three lighting db's the voltage disappears. The system is tns 3 phase
Has anyone had a similar problem before ?
thanks
 
Probably just a coupled voltage from other circuits running in close proximity. If it goes away when you switch off the other circuits then perform the tests like that. You could check the stray voltage with an analogue tester if you're worried about it, chances are it won't show a reading.
 