See this time after time - poor installation:

new split load board on a re-wire tt installation. The main switch is not a time delay rcd. The board is metal and there are split load single insulated conductors before the 30mA rcd's.

If these conductors touch the metal work the board may become live without the time delay.

Would this be a C2 or C3?
 
I kind of depends upon how much risk there is of a pre-RCD short to earth.

A well wired CU should be safe, but if it lacks an incoming gland or tails-clamp, and if it looks badly installed internally to the point where chaffed cables or loose to wiggle conductors are present then its a danger. The way I usually see codes are:
  • C2 = single & likely fault away from danger
  • C3 = multiple or very unusual fault away from danger
The BPG#4 has some guidance but its a bit vague in this area.
 
I would probably C3 it, based on no contact with sharp edges, all the terminations being tight, and no signs of any thermal damage. With all these being okay, I would say the odds of a L-E fault upstream of the RCDs is low.

Edit: just to add, the OSG 2.2.6 suggests (as you mentioned) a time delayed RCD as main switch, or an all-RCBO board. IMO, the same L-E fault we are concerned with in the OP can still occur with an all-RCBO board, should the CPC of an outgoing circuit make contact with the busbar.
 
Last edited:

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
north yorkshire

Thread Information

Title
EICR code for no upfront rcd on TT split load metal board: poor install
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
2

Advert

Thread statistics

Created
vde-electrician,
Last reply from
Pretty Mouth,
Replies
2
Views
1,174

Advert