See this time after time - poor installation:

new split load board on a re-wire tt installation. The main switch is not a time delay rcd. The board is metal and there are split load single insulated conductors before the 30mA rcd's.

If these conductors touch the metal work the board may become live without the time delay.

Would this be a C2 or C3?
 
I kind of depends upon how much risk there is of a pre-RCD short to earth.

A well wired CU should be safe, but if it lacks an incoming gland or tails-clamp, and if it looks badly installed internally to the point where chaffed cables or loose to wiggle conductors are present then its a danger. The way I usually see codes are:
  • C2 = single & likely fault away from danger
  • C3 = multiple or very unusual fault away from danger
The BPG#4 has some guidance but its a bit vague in this area.
 
I would probably C3 it, based on no contact with sharp edges, all the terminations being tight, and no signs of any thermal damage. With all these being okay, I would say the odds of a L-E fault upstream of the RCDs is low.

Edit: just to add, the OSG 2.2.6 suggests (as you mentioned) a time delayed RCD as main switch, or an all-RCBO board. IMO, the same L-E fault we are concerned with in the OP can still occur with an all-RCBO board, should the CPC of an outgoing circuit make contact with the busbar.
 
Last edited:

Reply to EICR code for no upfront rcd on TT split load metal board: poor install in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi all Called to do an EICR on a property 4 studio flats / bedsits within a single house. The t&e sub main to each flat runs within the fabric of...
Replies
4
Views
2K
Afternoon all, Just wondering what everyone's response to the following scenario is. Letting agents have asked us to carry out an EICR. There was...
Replies
42
Views
5K
Did a couple of inspections on 2 x 2 bed ground floor flood damaged flats today, only 4 circuits in each, bizarrely one socket circuit and 2...
Replies
6
Views
2K
Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K
Hello I live in a rental in scotland and have recently had an EICR carried out. I have an old fuse wire fuse board on a wooden plate with no rcd...
Replies
4
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock