J
JimLongDone
Hello,
My house has 25mm back boxes throughout, but I’ve noticed the previous owner has installed sockets and switches that seem to suggest/specify 35mm minimum. The sockets and switches do still fit flush on the wall, just that it is incredibly tight behind so the wiring has been routed meticulously to allow it to just about fit.
Our buyers are requesting an EIRC report to be done and I would like to know simply, will this been seen as a fail or a fault? Is this sort of thing specifically checked?
Thank you
25mm back box when buried in the wall may well be close to 35mm deep anyway. use a rule and a straight edge to see what the actual depth behind the wall face is.
Reactions: JimLongDone
Hi James,
That's right, but it's still below 35mm when I measured it, making it very tight and hard to screw in. I've heard that it's only a fault if the wires are actually damaged in the box though. Is that right, and that the depth wouldn't be a problem in itself?
Its an unusual thing for the home owner to check in any case. What made you want to check it?
An inspector will probably do a sample check and if squashed/flattened conductors are noticed but the IR tests are satisfactory, it may be recorded as an observation with a recommendation (C3). A low IR would indicate damage to the insulation has been done and a fault sometime in the future (possibly years) may be the result.
Wouldn't specifically check depth of boxes.
I think most manufacturers 'recommend' a minimum box depth but many accessories fit quite happily in a shallower box if the conductors are arranged to suit, and wouldn't show as a fault or low IR ...... resulting in Satisfactory EICR
If the cables are crushed and risk becoming damaged then yes, but it is very unlikely to be pointed out or checked and if the cabling is positioned in a way where it is not crushed it’ll be fine.
If things are neatly dressed in then it is often possible to fit things in smaller holes than recommended.
is it right?
No
is it likely to cause an issue?
probably not if it was done with extreme care and attention to detail
could it cause an issue?
yes, if the cables are crushed, deformed or pulled out of the terminals when screwing the fitting in place.
is it likely to come up as an issue on an EICR?
Probably not, but maybe depending if any of the above have happened.
Lets face it, if it is flagged up as an issue on an EICR, change the sockets to generic white ones for not a lot of money.
Reactions: JimLongDone and DPG
As above, I'm really intrigued why you checked it. I've got an idea why but I'll not say yet.
I checked it because I wanted to install a new one with USB before I went buying a load, but that requires a deeper box and after looking it became clear that wasn't going to happen. Appreciate all the info
Reactions: timhoward and DPG
There are USB sockets that only require a 25mm box (e.g. MK Logic K2744WHI).
Why bother upgrading with USB sockets if you are moving house?
Reactions: DPG
I looked at it before I decided to move house, but it's only a problem now that the new people want an EICR. You are rather a nosey bunch aren't you.
  • Funny
Reactions: freddo and DPG
I'd consider it something of a rare miracle if whoever does the EICR:
a) actually gets out of the van
b) actually took a socket off and looked behind it
c) even considered there might be an issue regarding depth of back box
....as there are an awful lot of cheap EICR certificate generating cowboys out there.
Even if you got a competent person, unless the socket is visibly not flush against the wall and 'looks wrong' I'd be highly surprised if it made it onto the observations list.
So I wouldn't lose sleep over this one.
Surely you can just change the one back that you have swapped though. Easiest way.