I do quite a lot of large condition reports.
I do exactly what the others mention, one EICR complete with schedule of inspections then as many continuation (schedule of test sheets) as there are distribution boards.
Its up to you how you choose to list it but personally If I have say a 3 phase supply coming into a 400amp switch then to a Busbar which feeds mutiple fused switches which in turn each feed a distribution board then I might tend to relable the boards so they make logical sense,
quite often I would do a test schedule for the busbar as well, I'd list the cable size/ and phase but just omit the results. Although it' not necessary I personally think it makes it easier to read in the future, with the early Amtech software you had to do this as it created a distribution board spider chart.
My labling would usualy be something simple like this.
Main Switch.
Busbar.
SF1 - supplying- DB1 - supplying a submain - DB1A
SF2. -etc-etc
Reasons being if you pick up the maintenance afterwoods, it makes it alot easier for you.
I was told at a ECA meeting once by a board member from the IET that strictly from a City and Guilds exam point of view that each set of distribution board test results should have a separate schedule of inspections. Personally I don't know anyone who does this, however if the condition report was carried out on a large Residential school then I would probably do separate Schedule of Inspections sheets for distribution boards that maybe supply wet rooms.
I would only do a separate EICR if there was a seperate incoming supply.
I do exactly what the others mention, one EICR complete with schedule of inspections then as many continuation (schedule of test sheets) as there are distribution boards.
Its up to you how you choose to list it but personally If I have say a 3 phase supply coming into a 400amp switch then to a Busbar which feeds mutiple fused switches which in turn each feed a distribution board then I might tend to relable the boards so they make logical sense,
quite often I would do a test schedule for the busbar as well, I'd list the cable size/ and phase but just omit the results. Although it' not necessary I personally think it makes it easier to read in the future, with the early Amtech software you had to do this as it created a distribution board spider chart.
My labling would usualy be something simple like this.
Main Switch.
Busbar.
SF1 - supplying- DB1 - supplying a submain - DB1A
SF2. -etc-etc
Reasons being if you pick up the maintenance afterwoods, it makes it alot easier for you.
I was told at a ECA meeting once by a board member from the IET that strictly from a City and Guilds exam point of view that each set of distribution board test results should have a separate schedule of inspections. Personally I don't know anyone who does this, however if the condition report was carried out on a large Residential school then I would probably do separate Schedule of Inspections sheets for distribution boards that maybe supply wet rooms.
I would only do a separate EICR if there was a seperate incoming supply.
Last edited:
). I guess I'm curious as to how it could get into that state and what the place is used for may help with some ideas.