Got to connect 4 x electric hand dryers tomorrow in 4 x different toilets. Was going to spur off the nearest socket point for each one, with an rcd spur by each dryer, via trunking/conduit.

Silly question, but do they need to be rcd spurred, if there is no shower???

Believe it or not they come with 3 pin plug tops. lol
 
toilet is not a special location, so the requirement for RCD protection only applies if sockets are fitted, as wiring is surface, so 522.6.101 does not apply.
 
so running a surge protected extension lead over the hand basin is a bad idea??? haha

i just thought because of wet hands, and the hand basin maybe rcd protection would be required, although i guess they are double insulated, although the be honest rcd spur units aren't cheap, and if i don't need to fit them then thats great
 
yes after reading some other forums i'm thinking it would be best to put the rcd spurs after all ;)
 
mount them high up then or they'll forever be getting switched off.
 
Never look for reasons NOT to install RCDs these days. Especially where water and the public are concerned, it's a no brainer!
 
i know this and was going to put them originally for peace of mind. just wanted to know peoples thoughts.

i underestimated their cost in my quote, but am sure i've allowed more than enough on the labour to cover them. i hope
 
Couldn't you RCD the entire circuit at the consumer unit with an RCBO or separate RCD, rather than having four individuals? These days I think it is normal to RCD everything, unless there is a very good reason not to.
 
I would have thought the sockets were on RCDs anyhow, personally I would wire the handriers on seperate circuits if it wasn't too much hassle, better Job IMO.
 
i know. that test button is irresistable.
 
its a small building that teaches english to foreigners. no rcd protection. fuseboards are old mcb types so you cant get rcbo's for them.

believe it or not the fuse boards for 2 of the 4 toilets are, yes you guessed it, in a door inside the toilet. lol. so could possibly supply them 2 direct from fuse board, although don't think there are spare ways
 
Fixed equipment, and not a special location, no need for RCBO unless disconnection times cannot be met IMO, however I would fit RCBOs if they were obtainable.
 
I would have thought the sockets were on RCDs anyhow, personally I would wire the handriers on seperate circuits if it wasn't too much hassle, better Job IMO.

agreed , 1 dedicated radial for all 4 driers would serve better.
 
Just a thought, do the manf's instructions stipulate RCD protection required? Daz
 
i haven't looked mate. but i'm gonna put them anyway for piece of mind. i've managed to fine some for £16 each at screwfix ;)
 
i haven't looked mate. but i'm gonna put them anyway for piece of mind. i've managed to fine some for £16 each at screwfix ;)

Make sure that the circuit that you are joining in to isn't RCD protected before you fit RCD spurs, or you may end up going backwards and forwards to reset one or the other due to discrimination.

Cheers.............Howard
 
its a small building that teaches english to foreigners. no rcd protection. fuseboards are old mcb types so you cant get rcbo's for them.

believe it or not the fuse boards for 2 of the 4 toilets are, yes you guessed it, in a door inside the toilet. lol. so could possibly supply them 2 direct from fuse board, although don't think there are spare ways

Do those 2 fuse boards supply the ring circuits for the 4 hand dryers your planning on installing?? If so, mount the two RCDs at the side of the CUs. That will serve your purpose and provide additional protection to the two ring circuits as a whole!! Material wise, cheaper too!! lol!!
 
i haven't looked mate. but i'm gonna put them anyway for piece of mind. i've managed to fine some for £16 each at screwfix ;)

At that price you'll definitely need RCDs and a Fire Extinguisher mounted at the side of it.

Edit
Oh I take you mean RCDs at £16 not Driers..
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Electric Hand Dryers
Prefix
N/A
Forum
Electrical Appliances & Whitegoods Forum
Start date
Last reply date
Replies
21

Advert

Thread statistics

Created
sl1210,
Last reply from
snowhead,
Replies
21
Views
6,177

Advert

Back
Top