Just purchased a new oven which has a 13amp fused plug attached. The kitchen has a cooker terminal which has 6mm cable coming from it. The existing oven has a 2.5mm flex (no plug). The hob is separate and also has a 2.5mm flex. Both oven and hob have been chocolate boxed to the 6mm cable - I did not do this!
So I want to be able to plug my new oven in and use the existing hob. The hob specs are 250v and 6kw - mania says to use 2.5m cable which is what the previous owner of the house has done. The new oven is less than 3kw.
Is it ok and proper to place a double gang 13amp fused socket on the end of the 6mm cable which comes from the terminal. Then fix a 13amp plug to the hob - attach the socket to the wall and have both oven and hob plugged in. This preserves the existing terminal in case the hob breaks and we need to hard wire one in the future. Is this ok to do?
you need to read the manufactures instructions and get a spark in to sort it out .
Why? I used to be an electrician but my info is from 17th edition and so is not current. I am a competent person but wanting confirmation that what I propose is ok. I am not proposing changing the electrics in the kitchen entirely, just a way to ensure I have both cooker and hob running off the same circuit ... manufacturers instruction aren’t worth the paper they are written on! It advises to plug into a socket in picture format; this is hotpoint!!
Agree with buzz. You need a cooker outlet for the 6k supply....and a separate socket for the 3k.
That existing is just a dangerous mess.....
It could well be a HOT POINT, going off your proposal.
I have to disagree on this point, as indeed your insurer may to find a get-out clause, in the event of manufacturer's instructions not being followed and a fire resulting.
I could argue I followed instructions and plug into a standard socket (which is never do!) ... point I was making is they are terrible instructions - more like Ikea instructions as no words, just pictures!!
[automerge]1569773576[/automerge]
[automerge]1569773612[/automerge]
In that case, if you refer to Section 5 of your 17th big yellow book and Appendix H4 of your on site guide, you should be good to go.
Looks like I’ll have to!
[automerge]1569773647[/automerge]
What’s the breaker size at the CU?
Is it sufficient to protect the 2.5 mm cable?
40 so yes
[automerge]1569773706[/automerge]
I agree it’s a total mess but I didn’t install any of that and I’m proposing taking it away to make it safe.
@Orisis_1982 I realise you've said you used to be an electrician but this is a pretty simple one so I'm guessing perhaps you didn't practise for very long, there is no disrespect meant here. I would feel uncomfortable giving advice to someone asking if it's ok to put a plug on a 6kW hob as it does show a lack of understanding of electricity and therefore you may make other errors, i.e not terminate tight enough, terminate too tight, have the wrong MCB, not have RCD protection (if required), no continuity of CPC, poor Zs etc etc.. These are all things the electrician would test when he connects up your oven and hob.
I know you want to do it yourself, but just spend £100 and get someone in, then you can be 100% sure it's safe (well 99%) rather than having that creeping thought at the back of your mind on whether you did it right.
[automerge]1569774343[/automerge]
Ps.. as for the manufacturers instructions I would say that the majority of the electricians on this site do take them in to account as the regulations state that we should. If we disagreed with them we could then state why on the minor works certificate that we issue and explain why we have not adhered to the regulations.
@Orisis_1982 I realise you've said you used to be an electrician but this is a pretty simple one so I'm guessing perhaps you didn't practise for very long, there is no disrespect meant here. I would feel uncomfortable giving advice to someone asking if it's ok to put a plug on a 6kW hob as it does show a lack of understanding of electricity and therefore you may make other errors, i.e not terminate tight enough, terminate too tight, have the wrong MCB, not have RCD protection (if required), no continuity of CPC, poor Ze etc etc.. These are all things the electrician would test when he connects up your oven and hob.
Thank you - when I purchased the house 3 months ago I was given all the manuals for the electrical appliances staying. The cooker and hob was 2 appliances staying (the make is one I’ve never heard of before). Both have been installed incorrectly. When reading the manual for the hob it states total power is 6000 watts however, it also states to use a 2.5m cable but also mentions using a ‘fused plug’. This is a mystery to me because my first thought was to add in a 1 gang socket for my new oven and the hob would be hardwired into the terminal - the 2.5m cable and mention of a plug has thrown me. Given how badly the job has been done previously I will get someone to take a look at it and will show them the hob manual and see what they say about it!! I suspect the oven and hob manuals have been translated into English because the language, sentence structure and grammar isn’t great. Saying that, hotpoint’s brilliant Janet and John picture installations aren’t great either ?
[automerge]1569775310[/automerge]
I see what you are saying ,but in those booklets it will say consult a qualified electrician ,and you thought you would ask us ,and looking at the pic you put up and we are not their, call somebody out to sort it out for you .
Thanks, I’ll have to because the existing is already a mess - I moved in 2 months ago and have had a bad time with the electrics and plumbing. Didn’t think to look how the cooker and hob was wired in! Until the cooker blew last week.
[automerge]1569775466[/automerge]
I’m not disagreeing with them but saying how bad the existing appliance instructions are, as I believe they have been translated, and the new oven instructions are just pictures and no words!!
Surprised diversity has not been mentioned.
If the existing cooker final circuit is 32A 6mm cable and if the new appliances come with manufacturers leads, chop off the moulded plugs (if its ok with manufacturer), use a Click dual outlet plate to connect both appliances. The existing outlet plate looks a bit tired, have this final circuit (and the rest of the house wiring) checked over by an electrician.
Bristol
United Kingdom
Electrical oven installation
UK
Deleted member 122464,
Deleted member 105166,