cornishboy
agreed, now I stick to Hager or Crabtree starbreaker have no problems and my loop readings are within acceptable values
You have to remember that the MFT is only injective 15mA into the earth on the no trip so that the RCD will hold and on the HI current loop it injects 25A which will give you a more accurate reading. Some of the RCD do cause issues so if you are not happy with your results link the CPC and Line conductors out at the far end of the circuit and test on high at the CU without it going through the RCD on the isolated circuit! I have had a few issues when testing Europa and BG RCD on the no trip with a 1552 and a stand alone loop tester ! You should have a good idea what your EFLI result should be from you dead tests IMO!Does anyone have issues with this test and how accurate is a No trip test?
I find my readings seem to change a fair bit testing the same circuit a few times.
This is using a 1730.
Proteus all the way for me!!!lol
British General ALL THE WAY SIR!