Ashley Poxon

Installed 3 new circuits in a 3 phase board all emergency and on key switches, the not em's will work with the key switches off. Turn a key switch on and the circuit trips, turn the next key switch on and that one will trip but if you reset the breakers and do the 3rd key switch it trips two circuits. I'm thinking it's something simple- I didn't do the dead nor live testing but if he's done it correctly then it passed. I was thinking maybe neutrals mixed up but it's not a split load board. The circuits are on rcbo's so could it be the ballasts? Wouldn't say loading as its only 7 fittings per circuit at around 4amps per 6A breaker. Any ideas
 
Since the non EM lights work OK and assuming there are more non EM than EM then the loading should not be an issue as you say.
However since the non EM lights work you cannot have the neutral from one circuit connected to the line of another as then the RCBO would trip on the non EM lights.
However if the line for the permanent supply to the EM lights were were mixed up then once the EM power supply was turned on the current would be supplied from one RCBO but returning via the neutral of another and so at least one would trip. IF they have slightly different trip times then maybe only one would trip,possibly both if they are similar, however this would be a full current fault and way over the minimum for an RCBO so instantaneous trip times only relevant
This would be especially likely if all the key switches are in the same switch plate.
With the RCBOs off then a continuity check from SL of a non EM light to the PL of an EM light (all switches on) should identify if this were the case.
 
Thank you Richard, it turned out to be a couple of little faults like an M4 gone into the perm live ect but the main problem was I belled out the perm lives to find they had mixed them up in the switch affectively giving each circuit 415v. Thank you again
 
Welcome to the Forum Ashley, we have an introduction thread if you wish to announce your new membership.
 
Can I ask Ashley, if there are normal/general light fittings on the new circuits or have you just put EM fittings on there own circuit? I take it you have installed self contained EM fittings?
 