Who thinks there is fire proof fixings within that trunking![]()
Now that you've mentioned it, I'm sure the OP will be opening the trunking lid to see.
Judging from the photos you have posted, I can't see anything wrong with this install. Tails are fine, correct type of RCD.
Did the electrician give you an Electrical Installation Certificate in respect of the work? If so, what type of earthing system has the electrician listed on the certificate in respect of the charger? TN-C-S or TT? Could you post a close-up photo of the charger?
Was the install carried-out through the OLEV Homecharge Scheme?
As the others have said the 10mm tails are absolutely fine. They meet the existing regulations as the maximum demand they can ever be expected to need is 32A. They also meet the requirements for fault protection.Hi,
We had a EV charger installed recently over the past day ie 32amp 7.2kw. In the fuse cupboard I’ve attached before and after photos.
I have a 100amp fuse for the house.
For the new EV board setup, should the 2 grey cables entering the EV board (10mm) be the same 25mm thickness as the other cables?
Would this cause any issues for me? Or is this against certain electrical standards?
Someone mentioned to me if I was to change the meter or DNO were to action any new improvements, that I’d have to get these 10mm cables changed before any work would be carried out in the future?
I have yet to settle on the work, so if there’s non standard work complete here due to this, I would be in a position to highlight and query the relevant electrical company. I would appreciate any advise?
Please excuse, as my knowledge in electrical stuff is non existent. It maybe that all is looks fine, and I’ve been given wrong advise.
Regards,
HY
I realise you have mentioned a number of times that 'someone' has told you they need to be 25mm but they do not. They would need to be 25mm if they were supplying your main consumer unit (even then they may not need to be).
I would be more concerned with whether an earth rod has been installed for this install. The EO website makes no mention that their unit can be used with the earthing supply you have (i.e PME) and therefore you should have had an earth rod installed. In fact the following link by EO states clearly you should have an earth rod installed for use with their unit.
lastly, it's easy for us to make mistakes as we are not there. I would ask the electrician who installed it if he has installed an earth rod and if not then why? He would hopefully quote one of the 3 exceptions from BS7671 722.411.4.1 but I think this is unlikely.
It's just that some "others" have specifically mentioned that tails need to be rated at 100AMP i.e. 25mm cabling; this was my initial concern?
So hence, I just wanted to clarify this?
Yes, lots of people get their regulations knowledge this way, by listening to 'others' who loudly proclaim their version or (mis) understanding of the rules as the truth.
There is a guide to the regulations which has a picture of a 'typical' domestic supply with 25mm tails feeding a single consumer unit which then supplies the whole installation. Many people fail to understand that this is just an example of a typical installation.
Is it possible to charge the vehicle when it is parked outside? Will the charge lead reach? If so it must be TTI'm pretty certain there is no external earth rod installed for this.
As the unit has been installed for use internally; is this perhaps the reason why no earth rod was installed or required?
Or does the vehicle have to be parked fully in the garage for the lead to reach? If so pme is fine.
The whole instal looks to be to a very good standard. I think the installer has done well and despite my previous post I wouldn’t be too concerned.
I did the EV charge course and the one thing that seemed contradictory was the placement internally of a charge point. If it’s parked inside on a pme the charge point should be pme if it’s parked outside it should be TT.
What happens if it’s both as yours is?
In theory changing the whole of the installation to TT which is way over the top. I don’t like that solution at all.
For this reason and other points I won’t go into I don’t install these units until a better safety system has been designed and built into the units.
Pete the whole install doesn't require TTing just the charging point in this instance.