W

wrinklyazza

went to job late today 2 new fans fitted with speed controllers working fine until you turn them up to max speed and it trips out. Then the whole site had gone down it hadnt just tripped the mcb but the mccc feeding the db. This happened twice was doing some investigating when the site agent said we had to leave site. got to go back tommorrow and carry on
 
start up current??? or are the fans too big for the OCPDs?? need more info. e.g. what does manufacturer specify ??
 
manufacter specifies dedicated supply which it is on they only pull 3.9 amps on start up and 3.2 amps when there running the controller is rated at 5 amps
 
so, cable size? OCPD rating? actual current measured with clamp meter?
 
check the other loads on it. could be on it's way out.
 
Could be just coincidence, I would be probably be looking elsewhere for the tripping problem if they're 3A fans on a 125A MCB. If it's not overloaded check the terminations aren't getting hot and check the main neutral terminations.
 

Reply to fan tripping breaker in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
1K
My circuit panel has two banks of breakers, each bank protected by an RCD. One of these RCDs has been problematic in that it trips intermitantly...
Replies
12
Views
1K
Hi all, I have been on a site repairing damage caused by travellers collecting copper for the last week. We have found and replaced cabling to get...
Replies
17
Views
3K
DIY query Have narrowed down the source of an occasional trip to one light circuit which is a varilight v-pro master dimmer slave set up. This...
Replies
0
Views
372
Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
501

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock