I am planning to move a socket outlet. The CU is largely unlabelled so don't know which 32 MCB to switch off. There are 2 x 32a MCB. All other mcbs are for lights (6a) and a dedicated immersion (16a).
To isolate the circuit, I tried switching off the first of the two 32a mcb which isolated some of the sockets but not the one I need to move. So I switched the 2nd 32a mcb off too (so now all/both 32a MCBs off but some of sockets still live.
So I tested RCD and main switch which tripped all sockets other circuits off.
I am assuming there is no cross over of ring circuits and that the 2nd circuit is not picking up a live from elsewhere (heavens forbid) although I then switched off all MCBs on all circuits and the 2nd 32a circuit was still live.
Can I conclude that the 2nd MCB is faulty and so not switching off and needs replacing or is there any other possible cause?
I'm an amateur so please bear with me and this is my 1st post.
How's that going to help?
From the OPs description it seems like he may well have some suspect wiring in place - an EICR would locate this, and also confirm which MCBs control which circuits, and also prove they are isolating correctly.
Update: This is my 3000th post !
Well for a start Dave it would prove whether the install has been interfered with or wired incorrectly, may seem expensive option, but better that than an unsafe install don't you think?
I think it is already quite apparent that there is a problem, an eicr won't fix the problem it will just tell you that it's there. It will also still be just as unsafe.
The fault, or at least the symptom is already known, the next step should be to find the fault surely?
Is it a flat?Did the main switch isolate your mystery socket?..Have you been unknowingly shareing with a neighbour.Try...main switch off..if all dead swop the 2 mcbs.And see if the same problem breaker is still passing through a voltage while switched off..Could the immerson circuit and a ring leg be mixed up.