Jul 15, 2016
84
liverpool
Hi guys
Hoping you guys could help. I have an 8 way RCBO board with all breakers used for dedicated circuits.
Ideally I would like to run a dedicated circuit to a new combi boiler I've had fitted rather than it be plugged into the ring main to prevent nuisance trips etc however as mentioned there are no spare ways.
one of my 16amp circuits powers just a washing machine and dish washer.
Another circuit, a 32amp is the kitchen sockets (3 counter top doubles) fed off a 4mm radial.
Would it be a ridiculous claim to disconnect the 16amp circuit wiring in the consumer unit and connect it up with the kitchen radial on the 32amp RCBO in order to free up the 16amp breaker so it can be used for the combi boiler
Hope this makes sense
Cheers
Hi adsmith. Is your washing machine/ dishwasher circuit powered by a single double socket, or 2 single sockets?
  • Agree
Reactions: GBDamo and Wilko
What other circuits and size of RCBO's have you got?
They'll be a better one than the Kitchen Circuit.
I’d probably put the dishwasher/washing machine on the kitchen circuit assuming it’s not to much grief extending the 4mm or fusing down for the 2.5...do you have any pics of the consumer unit and a bit of info on the house layout etc...there may be an easier way for you..
Reactions: DPG
You cannot do that. You would then have a 2.5mm radial protected by a 32A MCB and that’s not permitted. Especially as the two appliances are very high current.
The boiler will be fine powered on a 6A MCB. you might be able to re-jig the lighting circuits. Let’s see a pic of the consumer unit.
Reactions: pc1966 and Baddegg
There will only be nuisance tripping if there is a fault surely? Is there much earth leakage on the current RCBO it is on?
Reactions: DPG
Not sure why you want the boiler on its own circuit. Why do you think it will cause nuisance tripping?
I would advise putting the boiler on the ring circuit rather than messing up the existing circuit arrangements.
Boilers don't generally give much trouble with RCD tripping, at a guess I'd say it is more common for a washing machine to cause this than a boiler.
as above ^^^^^. spur off the RFC RCBO. can be done at a socket or back at the CU.
Reactions: EricMark
liverpool
Freeing up space in consumer unit
adsmith,
telectrix,