Re: Fuseboard replacement: Advice on minimum insulation resistance level for certific
cheers for shouting up guys and and happy new year - how ignorant of me lol!
The circuit in question was fully disconned out of board and no simple continuity tests flashed up between the circuit origin which i had removed completely and the rest of the board. I can understand a low parallel path if someone had pinched a P or N somewhere along the line but this circuit has no cpc at all throughout its length. Basically im getting a low reading between phase of the lighting circuit and the MET when the circuit has been removed?
whilst on the subject if you wouldnt mind, im not going to drag up all the crap about PIR's and competant schemes (im part p but not PIR bit) but can we clear this up:
Go to do a mains change. Surely you would have to do a PIR before changing board as I always do? If you aint PIR registered for domestics and it fails, then can you hand over the PIR cert? Luckily i have not had this problem yet.
Surely we all have to give a set price for PIR before we can price a board change and any other remedial action? I know i wouldnt want to be stuck with problems after agreeing a CU change price but ive heard many just change them and go from there simply on an initial visual! Is this how everyone else conducts business? I dont think we can risk pricing a CU change these days without doing PIR first as the results need logging anyway so they may aswell go on the installation cert at the end?
So this lighting circuit, if its near border line anyway (couple of M lets say), would you be happy reconnecting even on rcbo for tripping that circuit only? There is no damp or anything that could be causing the low reading back to the MET as far as i can see. sorry for babbling on!
cheers for shouting up guys and and happy new year - how ignorant of me lol!
The circuit in question was fully disconned out of board and no simple continuity tests flashed up between the circuit origin which i had removed completely and the rest of the board. I can understand a low parallel path if someone had pinched a P or N somewhere along the line but this circuit has no cpc at all throughout its length. Basically im getting a low reading between phase of the lighting circuit and the MET when the circuit has been removed?
whilst on the subject if you wouldnt mind, im not going to drag up all the crap about PIR's and competant schemes (im part p but not PIR bit) but can we clear this up:
Go to do a mains change. Surely you would have to do a PIR before changing board as I always do? If you aint PIR registered for domestics and it fails, then can you hand over the PIR cert? Luckily i have not had this problem yet.
Surely we all have to give a set price for PIR before we can price a board change and any other remedial action? I know i wouldnt want to be stuck with problems after agreeing a CU change price but ive heard many just change them and go from there simply on an initial visual! Is this how everyone else conducts business? I dont think we can risk pricing a CU change these days without doing PIR first as the results need logging anyway so they may aswell go on the installation cert at the end?
So this lighting circuit, if its near border line anyway (couple of M lets say), would you be happy reconnecting even on rcbo for tripping that circuit only? There is no damp or anything that could be causing the low reading back to the MET as far as i can see. sorry for babbling on!