Re: Fuseboard replacement: Advice on minimum insulation resistance level for certific

funny you should mention that - we had a big discussion about this on here a few weeks back and agreed its all pants!
Well at the time, funnily enough elecsa's website went down overnight for a few days without warning or even a message on their site saying saying down for maintenance - bad practice. anyway it now appears (correct me if im wrong) that they have removed the page about a seperate fee and assessment for PIR!! phew - just saved a lot of money!!! Not that i intended on doing it but i could of certainly quite easily tagged it onto my assessment last month for the sake of it!
well thats a step in the right direction then...but it might be like the "sales" in the sofa adds......like they will be having another "sale" of PIR assessments a few weeks from now...lol.....
 
Re: Fuseboard replacement: Advice on minimum insulation resistance level for certific

sorry my mistake, im sure i was either shown or read it somewhere. i bet i got confused with what you say regarding distribution circuits from same board etc. Ignore it - its late now!
 
Re: Fuseboard replacement: Advice on minimum insulation resistance level for certific

Sorry was talking about non 17th edition/no rcd protected boards like rewirables etc. Now that gives us the next pain of bypassing or disconn the rcd etc in a few years when it comes to more frequent PIR's on what is currently 17th edition installations- when we are on the 22nd edition and they have had a ton more cash from us!
 
Re: Fuseboard replacement: Advice on minimum insulation resistance level for certific

On a CU change, as opposed to a new build, I actually prefer to IR test the circuits individually, rather than a global test for a number of reasons.

a) in case there is something vunerable connected that I may have missed, such as an Alarm, aerial amplifier or central heating controls etc.

b) so I can check exactly which circuit may have deterioated or I may have problems with/need to rectify.

It does take longer to do this, but I have found it has saved me time in the long run.

Each to their own.
 
I'm with spark 68. On a ECR best to see what's really going on. Unless on the rare chance there all good on a lump test
 