Hi, I remember at college I was told that if you see old resettable cartridge fuses (the ones where a button pops out) to replace them - but I can't remember the reasons why??? I just said that they no longer comply to my customer but what actually is the reason? I hate not knowing and talking rubish!

And anyone know the BS number of these so I can put it in the quote?

Cheers.
 
Have a load on the van mate and will have you are your answer if no one lse can by tomorrow.
If you do change the box out, keep the button fuses, they plug into rewireable boards a treat for when you fault finding!!
 
yeah the Number is "BS OUT of DATE...." :D

not sure mate some bdy will pop up though

bs number of the new MCB flick switches is 60898
 
Last edited by a moderator:
I think you are talking about the old wylex MCB's (fuses are not resetable, once they have blown a new one is required) if so the bs number was; Bs3871 generally they only had a short circuit capacity of 1 or 2KA (M1 or M2)
 
Last edited:
I think you are talking about the old wylex MCB's (fuses are not resetable, once they have blown a new one is required) if so the bs number was; Bs3871 generally they only had a short circuit capacity of 1 or 2KA (M1 or M2)


Cheers, I can't tell from the pictures if that is the breaker, but the small short circuit capacity is ringing a bell - so I think thats it.
 
You lot are way too quick for my likings tonight...

Yep, 3871's. As far as I recall depending on the rating the breaking capacity was different. I think 5A were rated at 1 or 1.5kA, and the rest at 3 or 3.5kA, but it is clearly marked on the label or embossment (if there is such a word!) on the side....

Also, I seem to remember that there was a problem with the devices getting stuck closed due to the design.
 
Last edited:
Hi anybody tell me if old rewireable fuses and old bs3871's push button type and mcb's are all allowed within the same board (old wylex type)
 

Reply to fuses with a push button reset in the Australia area at ElectriciansForums.net

Similar Threads

Hi all, I am looking for some advice regarding old rewireable (3036) fuse boards in regards to additions and alterations. I am an electrician and...
Replies
28
Views
4K
I had a call to a new customer who was experiencing what sounded like nuisance tripping on a kitchen ring. Some background first. It's an MK LN...
Replies
4
Views
763
About 15 years ago, after having had a modern consumer unit fitted, and prompted by our electrician, I asked my then energy supplier (Tonik) if...
Replies
25
Views
5K
When I joined this forum a decade or so back, there was a discussion going on about a welder that was connected with a 3-core cable to L1, L2 and...
Replies
3
Views
2K
Doing one more of the flood of EICR today on a rented property before a tenant change, but ran into a slightly interesting case so would...
Replies
71
Views
13K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock