porticoman

I'm installing a garage unit but it's tripping the (20A) house breaker. There's no load on the garage unit so I'm missing something obvious/doing something stupid. The garage has pre existing T and E powering lights and a couple of sockets which I want to modify to get a bit of practice after doing Part P. The Wylex 2 way unit (1 x 6A and 1 x 16A) and a RCD is connected as per the instructions (yes,I've read them!) Line/Neutral into the RCD, CPC into the Earth bar and the pre installed neutral link is in place. I've checked the connections to they are biting the conductor not insulation, tight etc. When it's returned back to its original format (no garage unit) it works perfectly so I'm being dense and maybe not asking the right question. Anything constructive suggestions the forum could add would be great.

Thanks

Peter
 
I'm installing a garage unit but it's tripping the (20A) house breaker. There's no load on the garage unit so I'm missing something obvious/doing something stupid. The garage has pre existing T and E powering lights and a couple of sockets which I want to modify to get a bit of practice after doing Part P. The Wylex 2 way unit (1 x 6A and 1 x 16A) and a RCD is connected as per the instructions (yes,I've read them!) Line/Neutral into the RCD, CPC into the Earth bar and the pre installed neutral link is in place. I've checked the connections to they are biting the conductor not insulation, tight etc. When it's returned back to its original format (no garage unit) it works perfectly so I'm being dense and maybe not asking the right question. Anything constructive suggestions the forum could add would be great.

If tripping the 20A breaker (instantly presumably) with nothing connected to the new CU then there is a fault at the new CU that is connecting Line to either neutral or earth (or both). [If there is RCD protection at the house (shouldn't be, unless it is S type for discrimination) and that RCD is not tripping then the fault is Line to Neutral.)]
Make sure it is wired as in the right hand side of the diagram below, and check that there is not a break in the SWA Line that may be touching the case or the armour as it enters the CU (if it is metalclad).
RCD Board.jpg
 
Last edited:
Just another thought, what colours have you used for L, N & E? and do they correspond at the DB? Don't think this will be the prob but worth a look.

Rich
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Garage unit trips house consumer unit problem
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
41
Unsolved
--

Advert

Thread statistics

Created
porticoman,
Last reply from
Richard,
Replies
41
Views
9,719

Advert

Back
Top