Hi everyone,

Wasn’t here for a while, would like to get some opinions on my issue, if you don’t mind folks.
Gas bonding issue, gas incoming pipe is at one point and it’s boded as soon as it enters the premises, the meter is about 20 meters inside the premises, I have my boss insisting that bonding should be 600mm on consumer side after meter.
I know what regs say, but then they talking about standard installation where meter is at the same point where pipes enters the premises, which is not the case in these premises. It definitely needs boding at the point of entry as far as I am concerned, and I tested continuity across the meter between incoming and consumer’s pipework and had 0 ohms, so as it stands I am happy to leave as it is, but my boss insisting other vice.
I don’t see the point or need to install second bonding after meter, just because some CBRE gas compliance guy said so… Would appreciate your opinions. Premises are big office block. Thanks…
 
i would install a 10mm across the meter from the incoming pipe to the outgoing pipe. that way everybody should be happy.
 
i would install a 10mm across the meter from the incoming pipe to the outgoing pipe. that way everybody should be happy.
It makes sense if to keep all happy, but is this necessary? And obviously if to keep consistent I should install 50mm bond across as the original one, thanks
 
I don’t see the point or need to install second bonding after meter, just because some CBRE gas compliance guy said so…

Would that be Rob?
 
It doesn't actually state "consumers side" in BS7671 but where it enters the premises. To me there is nothing wrong and bonding across the meter is pointless.
 
Hi - with my tin hat on - OSG and GN8 show main protective bonding to gas on the customer side of meter. But as pointed out that leaves the substantial run of suppliers pipe inside the premises. Unless it's known this supply pipe is electrically through connected by the meter and it's fittings, then it sounds like an extraneous conductive part?
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Gas bonding comercial
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
6

Advert

Thread statistics

Created
bartkusal,
Last reply from
Wilko,
Replies
6
Views
1,541

Advert