I have a Generac GP8000e generator that I plan on back feeding the main panel of my home with the portable generator, power inlet box L14-30a and breaker. First, I will install an interlock between the utility main breaker and the generator back feed breaker. I will only use the L14-30 receptacle to power my home. (1) Do I need to ground my generator with 8’ rods etc.? and (2) Do I need to Remove the Neutral ground from my generator since my main panel already has that? Thanks again everyone.
 
I have a Generac GP8000e generator that I plan on back feeding the main panel of my home with the portable generator, power inlet box L14-30a and breaker. First, I will install an interlock between the utility main breaker and the generator back feed breaker. I will only use the L14-30 receptacle to power my home. (1) Do I need to ground my generator with 8’ rods etc.? and (2) Do I need to Remove the Neutral ground from my generator since my main panel already has that? Thanks again everyone.
First off never remove your neutral. Your generator will not work correctly without the neutral which means no 120vac. Not a great idea and you are not required to add ground rods on your generator frame since the neutral in the generators neutral is already bonded to the frame.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Michigan
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United States of America
What type of forum member are you?
DIY or Homeowner (Perhaps seeking pro advice, or an electrician)

Thread Information

Title
Generac GP8000e/Need to be grounded? Remove Neutral?
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
1
Unsolved
--

Advert

Thread statistics

Created
jamilmwendwa,
Last reply from
Megawatt,
Replies
1
Views
1,248

Advert

Back
Top