I changed an old fuse board for a new consumer unit and the lighting for this house was connected in two separate fuses. So I swapped one for one and put them into two 6 amp breakers. Now the light at the bottom of the stairs is permanently on and the light at the top is off. Light at top controlled by two way switching. Light at the bottom just controlled by single switch! I think it is possibly one big ring as I am getting cutlrrent on the other when only one is connecting into a breaker?
 
There was a separate little fuse board that was fed with other tails, it contained two lighting sized cables but contained no fuses so I simply put them in a junction box to ensure they weren't made live. Apart from this It was a simply swap
 
There was a separate little fuse board that was fed with other tails, it contained two lighting sized cables but contained no fuses so I simply put them in a junction box to ensure they weren't made live. Apart from this It was a simply swap
And have you checked to see if they are live with your new board powered up. The neutrals in this old board are they now separated.
 
And have you checked to see if they are live with your new board powered up. The neutrals in this old board are they now separated.
I checked for voltage on the live conductor and it wasn't live however I may have neglected the neutrals, they are not seperated. I also tested the light that is permanently on and the current is not coming from the switch live but instead from the neutral
 
Was the old consumer unit with no fuses fitted actually switched on.
 
Is there voltage between the apparent redundant neutrals and the neutral bar in the new board when the lights are on.
 
If you have voltage between where I suggest those conductors may not be redundant, only guessing mind you.
 
It would make sense as nothing else has been touched apart from the board change, so it must be something I have physically done I guess?
 