I would say that you have an armour strand, at one of the glands, inside the gland and nearly piercing the line to give the low (ish) IR reading line to earth.
The RCD tripping I would say would be a neutral on the wrong side of the RCD in the CU.
 
Glen don't be so sensitive lol!
Identified the damned circuit with the problem tested it pulled it apart put it back together swore at it in several languages etc.
All connections checked and there's plenty of room to look. Just can't find the fault.
I've only a few years experience compared to some on hear with decades so I'm asking for "ideas/suggestions/help
Now b...cks was more a comment hence my comment in return.

If I can't find the problem I will call in a fresh pair of eyes to review what I've done. Any one on hear in the Suffolk area???
Cheers
 
or a N-E reversal somewhere.
 
Glen don't be so sensitive lol!
Identified the damned circuit with the problem tested it pulled it apart put it back together swore at it in several languages etc.
All connections checked and there's plenty of room to look. Just can't find the fault.
I've only a few years experience compared to some on hear with decades so I'm asking for "ideas/suggestions/help
Now b...cks was more a comment hence my comment in return.

If I can't find the problem I will call in a fresh pair of eyes to review what I've done. Any one on hear in the Suffolk area???
Cheers


think you have me mixed up with someone else there fella....lol....

i was trollin a bit...but not in a bad way...

look...the fault is there someware...isn`t it...

first ramp the RCD...check that...

once you have eliminated that then move on....

Richard has made a good point about one of the armour strands...

you will have to seperate each section of this install though till you find it...as long as the RCD is OK...then there is a fault here....
 
Richard Burns the armour strand is a good suggestion re the low IR thanks. I'll check the 4 external glands.
Re the RCD neutral is definitely on the right side.
 
Disconnect the first junction box that the SWA goes to after the CU, and test that. If that is ok, disconnect the 2nd JB after the CU and test from CU to there.....and so on......the fault must be there somewhere!
 
Rip it all out, move the pool thingy closer to the house and use a continous piece of external grade T&E. If you cant get the right thickness double it up in parallel to make a nice loop. Just make sure you tie wrap it together. Problem solved, especially if you sack the RCD protection idea!
 
Telectrix thanks for the suggestion I've looked but will look again and re check. Currently live and neutrals well separated into Henleys with earths into brass 4 or 8 way "Met" connectors.
Always possible in the cold and damned rain I cod's it up!
Cheers
 
If it is raining as you install that could be another cause of low IR readings, water tracking between connections, not very likely with henleys and you did say the boxes were dry, but 10Mohm is a good candidate for water.
 
Glen don't be so sensitive lol!
Identified the damned circuit with the problem tested it pulled it apart put it back together swore at it in several languages etc.
All connections checked and there's plenty of room to look. Just can't find the fault.
I've only a few years experience compared to some on hear with decades so I'm asking for "ideas/suggestions/help
Now b...cks was more a comment hence my comment in return.

If I can't find the problem I will call in a fresh pair of eyes to review what I've done. Any one on hear in the Suffolk area???
Cheers

I would wet myself it was GLENNSPARK :biggrin5:
 
he sure does know. it's somewhere outside of leeds.
 
Oh no he's not from Leeds is he?
If so Mr Glensparks I do apologise for what I said earlier.
I used to live up North.
 