A
Allan White
Hi all... I'm new here and already looking for help with an odd request :)
I'm looking for a lockable double pole switched fused spur suitable for domestic installation... does anyone here know if such a thing is available?
Even an hour with Mr Google doesn't turn anything up and I really don't want to fit an industrial red/yellow double pole 'rotary' isolator between the spur and a new CHP boiler (how many woman would have that in a kitchen???).
BTW the reason I'm asking is that I work in the micro CHP field and the upcoming G83 requirements will mean all micro CHP boilers will require a lockable double pole isolator to be fitted. Note this is subtly different from the current regs which require a securable dp isolator (eg a domestic switched fused spur).
Thanks in advance y'all
Allan
Mk do a padlockable 13amp FSU... ive seen the metal clad surface versions but they may do a standard white top version.
Upvote 0
if it specifies a lockable isolator then a fused spur wont be required, a normal isolator will do and they are readily available.
Upvote 0
OP states he wants a DP fuse spur, the circuit design may be such that it needs fusing down, he looking for a kitchen asthetically friendly one at that so it looks like a standard FSU, if you know of any readily available that meets the OP's requirements then pls forward a link as i have only come across surface mount padlockable metal clad versions.
Upvote 0
If there is going to be a demand for them, manufacturers will start making them.
They may already have them under way.
Have you tried contacting Mk and the like directly?
Upvote 0
Incidentally for those following this thread that might not be aware - conecting a micro chp to a ring circuit requires the ring fusing to be downrated to 25A...
If your connecting to a ring circuit your FSU would be your fusing down as would a plug top if directly plugged in, not all brands of DB have a 25amp fuse range so cant quite understand where this is coming from, you cant have a product demanding an alteration to existing circuit design (the ring in this case) that is fully compliant and fused at 32amp, if this is the case the manufacturers should be stating that its not to be connected to the ring main. Any contractor following and maybe doing work on or testing the ring will quite rightly state the 25amp although safe would benefit more with a 32amp fusing not aware that 1 product attached has created this situe.
Upvote 0
Hang on this has gone from a fused spur 13a max to a 20amp switch rated at 25amp from the ring, sorry its friday and i must have missed something.
Upvote 0
Could you not use a 3pole fan isoaltor as they are lockable?
Thanks Dillb. Good idea - I've not really searched for 3 pole switches. Do you have a make in mind and would it be suitable (and by that I mean aesthetically suitable) for domestic use? I don't recall seeing anything 3 pole that fits an existing patress...
Upvote 0
Im with needasparks here.... you stated a sw/fused spur in your opening post that would fuse this circuit down anyway, you have been shown by myself and archy of the option of a standard household sw/f spur by MK that is lockable and although no disrespect to Dillb here but his method contradicts what you originally asked for, can you please enlighten us to exactly you are after Allen?
I'm looking for a lockable double pole switch fused spur!
Upvote 0
Hi Darkwood - thanks for the reply
Apologies for the edits - I'll get the hang of this forum soon!
I've looked at these and they are similar to their white versions. Yes they are indeed padlockable by pulling out the fuse carrier. Unfortunately the requirement is for a lockable double pole isolation and it is possible to switch these (and other makes) with the fuse out which means that it in effect only one pole that is 'locked' out. I've not seen one but I believe it is possible to get a bar which fits through the fuse carrier to stop switch operation but these only count as securable and not lockable (that subtle difference again...).
Upvote 0