Discuss Immersion Heater - PV electricity in the Central Heating Systems area at ElectriciansForums.net

Ray you have my email address, lets coresspond via external means.

As long as the PV system has been fitted a certain way and you can put the equipment in a "box"
(to suit your location) . Not installations have the room to mount everything. The rest is easy.

Andy

Hi Andy
We've just had a PV system installed by Rayotec (commissioned on 9th June) with generation meter etc. in the porch and tails going direct to outside meter box. Like Ray I'm not an electrician but reasonably competent and very interested in assembling and installing the controls you have described in these posts. We have an indirect hot water cylinder fitted with with 3 kW immersion heaters top and bottom formerly controlled by Horstman Economy 7 timer. Would you be able to supply the bits and instructions? Thanks, Brian
 
Like a drill speed controller or light dimmer a phase angle controlled immersion is going to radiate some electrical interference, only worse because of the larger current and long cable between the immersion and fuse box. What sort of suppression is going to be needed to stop interference with say radios and TVs?
 
Well a drill has an arc across the com that is suppressed by a capacitor, but I am not sure that there will be any problem with this. I have been testing my circuit on 3 kw immersion heater with the triac control and have had no problem at all.
 
Like a drill speed controller or light dimmer a phase angle controlled immersion is going to radiate some electrical interference, only worse because of the larger current and long cable between the immersion and fuse box. What sort of suppression is going to be needed to stop interference with say radios and TVs?
This is an interesting article which discusses this aspect http://bit.ly/m1sLDY
I think that it's not so bad with resistive loads.
 
Hi Millerman. Forgive me but burst firing will pull full power for a determined number of cycles. (see Burst firing ) This will then give a draw from the grid and then the cycles shut off for another set period. This is only useful for the power control of a heater temperature not what you need for balancing a load. I have just completed my circuit that measures the two power levels ( current coils, no need to phase reference if you go on output from dist board, several cores can fit through one coil no problem, remember to only use one from each ring circuit ) compares them and provides an output via the triac. It keeps the house just exporting a small amount of power whilst dumping what else is free into any resistive heating load. I used a 741 to compare the two signals, pass this onto another 741 which adds a reference voltage ( zero point ) and adjusted the gain via pot on feedback gain to alter the slope, thus totally analogue and very cheap. No problem with EMC at all. It can only do this by working at a cycle level. Burst mode will cost you power consumption sorry.
 
New posts

Reply to Immersion Heater - PV electricity in the Central Heating Systems area at ElectriciansForums.net

Similar Threads

Hi, Small flat, currently has a small'ish feed water tank, top of a cupboard, feed through a wall into under stairs cupboard. Hot water tank...
Replies
5
Views
483
The unit only heats water using the programmed boost and when pressed in the 1 2 or Cont boost function. I have checked the off-peak time which...
Replies
7
Views
435
I have taken delivery of an undersink water heater. It is fitted with an RCD on the electrical supply cable which terminates with a euro-plug. I...
Replies
19
Views
2K
Hi, Have normal fused immersion heater switch. I would like to add a smart wifi switch to it so when my Solar is producing over 3k spare, going...
Replies
2
Views
2K
Hi All. Its been ages since I have been on here- Fortunately log in details stored on PC. I have just had a new boiler and 210 ltr unvented tank...
Replies
9
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock