Hi - I have a Warm-up underfloor heating system. And it's stopped working. I did a basic resistance check - and clearly there's a problem (shows just 18ohms when it should be nearer 200). Warmup have said they can send an engineer around to lift a tile after doing a thermo heat check. However, they said the best thing to do first is an insulation resistance check... Never done one before, but I see there are some meters online for around £35. I'm assuming to do this you:
  1. Turn off mains
  2. Remove warmup live, neutral, earth cables from connecting to the mains (completely isolates the heating elements/Warmup system)
  3. With the tester and isolated system, test:
    1. live/neutral at 1000volts;
    2. live/earth at a 1000 volts
  4. Reading should be around 200 megaOhms.
Is this correct - or is it even worth doing, given the floor isn't heating anyway...??

thanks for any advice
Rob
 
Do you know a local electrician with test equipment?
The ones we use are calibrated yearly, and cost a lot more than £35.
 
Will the £35 ones give out 1000V?
A pro tester will give 250v, 500v and 1000V
What did you use to get your 18 ohm reading?

If the engineer is coming out, he will have the required tester needed. Is the system under warranty?
 
what is the area of the mat, in sq.m.? 18 ohms equates to about 3kW which would be 15 - 20 sq.m.
 
Do you happen to have kept the booklet from when it was new and installed? There’s a table showing the target resistance for the various sizes of mat and a section where you record the resistance before cutting it and sticking it down.
 
Telectrix/Tony: it's only 2.5sqm really. It's the warmup loose-wire UFH - DWS400, with the expected resistance of 128 Ohms (i'm only reading under 20..) See second row in table attached
thanks all...
Rob

Capture.PNG
[automerge]1567806513[/automerge]
Littlespark: the insulation resistance tester was this one...: here
The system is only under warranty if when Warmup turn up they find a fault with the unit. However, I can't see how they'd identify whether it's the UFH wiring being at fault or was caused by the tiler (me...) nipping the cable whilst originally laying the floor. I just get a feeling they'll say it's not their product - which'll cost £300 to find the fault, lift the tile and fix it.. I will still have to make good and retile.
 
As an Amazon Associate we earn from qualifying purchases.
Telectrix/Tony: it's only 2.5sqm really. It's the warmup loose-wire UFH - DWS400, with the expected resistance of 128 Ohms (i'm only reading under 20..) See second row in table attached
thanks all...
Rob

View attachment 51935
[automerge]1567806513[/automerge]
Littlespark: the insulation resistance tester was this one...: here
The system is only under warranty if when Warmup turn up they find a fault with the unit. However, I can't see how they'd identify whether it's the UFH wiring being at fault or was caused by the tiler (me...) nipping the cable whilst originally laying the floor. I just get a feeling they'll say it's not their product - which'll cost £300 to find the fault, lift the tile and fix it.. I will still have to make good and retile.
i'd not bother with that cost . just buy a pair of woolly socks.
 
As an Amazon Associate we earn from qualifying purchases.
Hi - not doubting your measurements, but have you checked the fuse has not melted? Someone on here may be nearby and be willing to test the ufh for you, if you’d like.
 
Hi - not doubting your measurements, but have you checked the fuse has not melted? Someone on here may be nearby and be willing to test the ufh for you, if you’d like.
Wilko thanks. Think the only fuse is the 13amp to the unit. I’m getting mains power to it and the thermostat is working fine. So assume that’s everything. anyone who’s in the south west London area is welcome. Based in Fulham. Thanks again...
 
if the element is shorted giving 18 ohms, it will pull 13A an the 18ohm section will get hot.
 
Tony thanks. The FCU has a 3A fuse ((checked it yesterday) and is working fine. There’s also a 5A fused socket just ahead of the thermostat... if that makes sense.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
London
What type of forum member are you?
DIY or Homeowner (Perhaps seeking pro advice, or an electrician)

Thread Information

Title
Insulation resistance check
Prefix
N/A
Forum
Electric Underfloor Heating Wiring
Start date
Last reply date
Replies
12

Advert

Thread statistics

Created
Rob Alldis,
Last reply from
Rob Alldis,
Replies
12
Views
8,673

Advert

Back
Top