To be honest the problem reported by the OP is not one I have ever experienced.
If I need to disconnect appliances from a circuit so I can test it, they get disconnected.
Never had anyone complain about me having to do so.
BS7671 requires us before undertaking an alteration or addition to first determine that the existing equipment (including the supplier's) and earthing arrangements are adequate for the proposed new work.
There is no requirement to issue any certification or a report when doing so.
Once new work is completed, appropriate certification along with the results of any relevant tests is required to be issued.

How people determine that the existing installation is adequate is up to them.
Some will want to test the complete installation, others just the circuit being altered.
With an RFC, I would suggest it's a good idea to first check that it is in fact an RFC, that there are no breaks in the ring, and depending upon the alteration, whether RCD protection will be required. if yes, then an IR test would be to my mind a good idea.
In the OP's case, there is no requirement for RCD protection.
As such all that will be required, is an MWEIC recording the IR of the new conductors, the Zs and that polarity is correct.
The Zs test will prove continuity of the CPC.

Lets CUT OUT some of this WORDY RUBBISH


AT no POINT did you make say you were checking the CPC was Connected before you TURNED it ON.


AS it says on the "MWEIC"
ESSENTIAL TESTS
Earth Continuity Satisfactory
Insulation Resistance L-L and L-E
Earth Fault Loop Impedance
Polarity satisfactory
RCD Operations

spose to make sure a circuit is OK before POWERING.

As far as i know all this POST was GOING ON ABOUT, was asking about is the IR results OK!!
 
To be honest the problem reported by the OP is not one I have ever experienced.
If I need to disconnect appliances from a circuit so I can test it, they get disconnected.
Never had anyone complain about me having to do so.
BS7671 requires us before undertaking an alteration or addition to first determine that the existing equipment (including the supplier's) and earthing arrangements are adequate for the proposed new work.
There is no requirement to issue any certification or a report when doing so.
Once new work is completed, appropriate certification along with the results of any relevant tests is required to be issued.

How people determine that the existing installation is adequate is up to them.
Some will want to test the complete installation, others just the circuit being altered.
With an RFC, I would suggest it's a good idea to first check that it is in fact an RFC, that there are no breaks in the ring, and depending upon the alteration, whether RCD protection will be required. if yes, then an IR test would be to my mind a good idea.
In the OP's case, there is no requirement for RCD protection.
As such all that will be required, is an MWEIC recording the IR of the new conductors, the Zs and that polarity is correct.
The Zs test will prove continuity of the CPC
.
This is one of the most pointless 'discussions' I've ever seen on this forum.
If a new addition is connected to an existing circuit then that circuit has been altered and should be tested AFTER the alteration to ensure compliance. What you are suggesting is testing only the addition PRIOR to connection, and testing the existing before any work takes place. This takes no account of a fault introduced when the addition is connected to the existing circuit!
 
Spin being pedantic has caused a debate over nothing.......clearly we all know what happens with regards to testing and issuing EIC's and MWIEC's, Spin just decided to 'spin' it a bit........
 
Guys enough with the petty comments, all it does is derail the thread so either keep it on track or it will be closed.
 