Hi all,
I'm sure this question has been asked before but just can't find it.
When doing the IR test on a 3phase commercial board, how do you go about testing the circuit if there are items that just can't be disconnected, ie Bank of lights or immovable equipment, is there a trick to doing this?
Have the same issue with domestic single phase boards and high ceiling downlights!

Any advice would be much appreciated, TIA
 
Whether single or three phase you follow the same principle connect line and neutral together then test to earth.
That's what I've been doing by way of a "piggy back lead" on my megger mft 1721, but get unsatisfactory results. I have also confirmed this by testing with a load on the circuit (oven circuit)...unsatisfactory, then taken the load off and voila satisfactory.

The problem is I'm getting handed more & .more EICR'S where I can't remove the loads, especially in commercial settings!
 
What are the unsatisfactory results, don't forget on a periodic you aren't looking for perfection.
 
Most commercial loads should have a local isolator. Turn it off and test to there.

domestic eicr forms have a box to list equipment likely to be damaged due to IR testing…. LED lights, smoke detectors etc. Just have to note as a limitation.
 
0.09M.ohm very much unsatisfactory
In this instance it is what it is. I tend to have a quick look but all you can do is Code it in the Report. There is little which should affect an IR test unless you have a genuine fault whether this be the cabling or a light fitting but rcd sockets and spurs can, filtered equipment will normally test clear at 250v.
 
As above.
This is most probably a fault. You're not doing anything wrong, it gets coded and then it's up to the client to get it fixed.
You just cant feasibly disconnect everything, therefore L/N - E IR test, as you are doing.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
St Albans

Thread Information

Title
IR testing with a full load?
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
9

Thread Tags

Advert

Thread statistics

Created
Eugene Herbst,
Last reply from
HappyHippyDad,
Replies
9
Views
1,113

Advert

Back
Top