Hi All, first post here and looking for a bit of advice. I am planning on having a few changes done to the kitchen island.

wanting to add a quooker tap.

This is what I currently have in place;
Stating at the CU.

40a mcb > 10mm2 t+e > 60a junction box (at island) > 10mm2 t+e > 45amp mk switch > 7.8kw induction hob.

A few years ago when the extension and kitchen was done I asked for the cable to oversized to accommodate future changes incase we wanted extra hence the 10mm cable.

I have had local spark have a look and this is what he a suggested.

Swap over to a 50a mcb split the cable at the island a take a 10mm feed to a 20a switch and add the tap to this.
The spark has said it's a push getting 2 10mm cables into 60a junction box, he has suggesting using either Henley blocks inside an enclosure or using wago din terminals to split the 10mm cable.

I want to known what's the best option not the easiest or cheapest before I go back.

Any advice is much appreciated

Cheers
Matt
 
whatever your electrician decides what is viable and safe. can't see much difference in cost with either option. might be beneficial to add a MCB for the tap circuit instead of a 20A switch.
 
True, but then I would bypass the RCD and have the whole island on RCBO's, but then I would have the whole house on RCBO's, I am a fan of them. Still no smilies, pretend I put one on with a tongue in cheek.
 
Thanks for your replys, I've just been and checked and the board has 2 80a RCDs fitted if this makes any difference?
that would indicate that all your circuits are RCD protected. half on each RCD. whichever way your electrician decides to proceed will not make much difference to cost.
 
What Welchyboy1 said
The Quooker is only 1.6 or 2.9 (if you get the big one) kW and the instructions say to use a 13A socket.

If you can't just change to a switch with a socket, then just add a single socket as a branch of the radial - it does NOT need to be 10mm cable. Assuming it's only short, then it actually only needs to be 1.5mm to feed a single socket - as the plug is fused, the cable feeding the socket is protected by this fuse and the regs allow for the cable to be smaller than would otherwise be needed for the upstream MCB rating. The biggest problem will be terminating it alongside a 10mm cable into the terminals in the JB.
 
Could he just not come of the 60a terminal block with 2.5mm to a fused spur or single socket ? Looking at the cable would only be half a meter long ?
I did ask this and he insisted it needs to be 10mm to the socket or spur and this is the cable feeding the island that's when blocks or din terminals was mentioned to split the 10mm into 2. But the switch with socket sounds like this is what I need.
 
I did ask this and he insisted it needs to be 10mm to the socket or spur and this is the cable feeding the island that's when blocks or din terminals was mentioned to split the 10mm into 2.
Go and find yourself an electrician ;-)
The person you have consulted may call himself that, but he doesn't know what he's talking about.
That's about as polite as I can put it !
 
Go and find yourself an electrician ;-)
The person you have consulted may call himself that, but he doesn't know what he's talking about.
That's about as polite as I can put it !
I'm going to get someone else to have a look me thinks, I have just spent the last few hours looking through regs and other questions people have been asking regarding similar situations.

As far as I can see taking a spur from the 10mm would be fine providing it has rcd protection, not excessively long and providing the cable has no risk to damage which it hasn't it will be inside the center of the island.

If the tap was to have a fault then the fuse in FSU or plug would protect the cable am I correct ?

By the way the tap is 1.6 kw.
 
If you upgrade the mcb to 50A(like you previously mentioned), overload protection would be satisfied with a fixed/fused load but maybe fault protection of the cable would come Into play regarding the size of cabling you use between the 10mm and the spur?

what would be the minimum size that could be used?(I’m not sure just hypothesizing)

'no risk of damage' is a bold statement in this game with the muppets that are working in and around it lol!
 

Reply to Kitchen island power requirement change in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

The ongoing kitchen refit..... I have chased and fitted 10mm T&E from the cooker outlet to the isolator switch and up into the loft. I have 4...
Replies
4
Views
1K
We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
584
Evening all, Been to a job on Fri where the customer had a condition report completed. Two of the remedial identified was that there were too...
Replies
7
Views
1K
DIY'er question: I have a singe switched fused spur above my kitchen counter, providing power to an undercounter fridge socket beneath it. The...
Replies
2
Views
356
Hello hope you can help I have a single oven 2.4kw max and a ceramic hob 6kw max I would like to put then both on the same circuit so i was...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock