Hi All, first post here and looking for a bit of advice. I am planning on having a few changes done to the kitchen island.

wanting to add a quooker tap.

This is what I currently have in place;
Stating at the CU.

40a mcb > 10mm2 t+e > 60a junction box (at island) > 10mm2 t+e > 45amp mk switch > 7.8kw induction hob.

A few years ago when the extension and kitchen was done I asked for the cable to oversized to accommodate future changes incase we wanted extra hence the 10mm cable.

I have had local spark have a look and this is what he a suggested.

Swap over to a 50a mcb split the cable at the island a take a 10mm feed to a 20a switch and add the tap to this.
The spark has said it's a push getting 2 10mm cables into 60a junction box, he has suggesting using either Henley blocks inside an enclosure or using wago din terminals to split the 10mm cable.

I want to known what's the best option not the easiest or cheapest before I go back.

Any advice is much appreciated

Cheers
Matt
 
whatever your electrician decides what is viable and safe. can't see much difference in cost with either option. might be beneficial to add a MCB for the tap circuit instead of a 20A switch.
 
True, but then I would bypass the RCD and have the whole island on RCBO's, but then I would have the whole house on RCBO's, I am a fan of them. Still no smilies, pretend I put one on with a tongue in cheek.
 
Thanks for your replys, I've just been and checked and the board has 2 80a RCDs fitted if this makes any difference?
that would indicate that all your circuits are RCD protected. half on each RCD. whichever way your electrician decides to proceed will not make much difference to cost.
 

Reply to Kitchen island power requirement change in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello All. I'm quite new to this game and gaining experience, but going well in the main. My customer wants to feed a Hob ( on island in centre...
Replies
5
Views
236
Hi, I have a book on domestic wiring which says that everywhere there is a change in current carrying capacity along a circuit there must be some...
Replies
3
Views
279
The ongoing kitchen refit..... I have chased and fitted 10mm T&E from the cooker outlet to the isolator switch and up into the loft. I have 4...
Replies
4
Views
1K
We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
669
Evening all, Been to a job on Fri where the customer had a condition report completed. Two of the remedial identified was that there were too...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock