Hi All

Can someone please clarify for me? I have installed a circuit on a TT system but the gas and water only have 6mm bonding. Does this mean I have to upgrade it or just note it on the cert and advise the customer?

Many thanks
 
If your main earthing conductor is 10mm then 6mm is fine for the main protective bonding conductors and would not need to be noted.

If your main earthing conductor is >10mm then note it on the cert it will only need replaced if it shows evidence of thermal damage.
 
I thought the main earth (ie to the rod) only needed to be 2.5mm (4mm if no mech protection) for TT so 6mm main bonding is ok.

It is as Sintra said -The main protective bond on a TT must be a min of 6mm² and not less than half the size of the main earth. You are correct in saying that the min size of an above ground main earth is either 2.5mm² or 4mm² depending on mechanical protection, but if someone has unnecessarily installed a 16mm² that would take the MPB up to 10mm² - in which case you would do a risk assessment checking for overheating of the MPB and note on the cert if you wanted to stay it as 6mm² :)
 
thanks everyone main bonding is 16mm so technically is should be so 10mm then as I thought as half the size, the meter is outside - will have to upgrade i guess to be safe after i do a a risk assessment of course - thanks again all

ps not sure why they used 16mm as its only 2 meters from the meter!
 
could be cheaper to just reduce the size of the main earth lol maybe the last guy only had 16mm² on board or didn't know the regs for a TT :)


Edit - i really must type faster eh Tel? lol
 
Last edited by a moderator:
The actual size of the earth conductor doesn't matter.
It's the size that is required that matters.
So if after applying the adiabatic equation, it is determined that only 10mm² is required, but someone has installed 16mm². You still only need 6mm² for the bonding.
 
Last edited by a moderator:

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Leave 6mm Bonding on TT?
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
14
Unsolved
--

Advert

Thread statistics

Created
cyberjunction,
Last reply from
Spudnik,
Replies
14
Views
5,634

Advert

Back
Top