Hi everyone,
I have recently replaced 10 old strip lights in a church hall with new LED strip lights.
I ran an insulation test and all seemed good. I switched them on and all seemed good.
I had a call from the vicar to say that they are not working so went back to site to find the MCB had tripped. I retested and all was good. When I reset the MCB they come on. The light switch works fine. They go on and off. After an hour or two the MCB has tripped again.
Something Im missing? They are 60 watt equivalents and I have checked each connection to make sure there is no issue.
Bit at a loss now as to why this keeps happening. The Cons unit is pretty old and Ive tried a different breaker to rule out that. Im guessing it is insulation but not sure as to why when my readings are >500.
Thoughts appreciated
Thanks