sparky1966

Hi everyone,

Can someone please help me. A local house wanted some emergency lighting putting in so when i went and had a look at the consumer unit it had the upstairs lighting circuit on a 6A mcb and the downstairs on a 32A mcb. The CU has NICIEC stickers all over it.
Am i missing something or should the lighting circuit be on a 6A mcb?

My next problem would be that there are no spare mcb slots and there is no room to put in a new board. Any advice on this as well please. (Can both lighting circuits be put in the 6A mcb providing calculations are all ok). (I presume this would be safer than having it in the 32A mcb). (There will be emergency lighting if the 6A mcb holding the 2 circuits cutout)

I appriciate your time on looking at my question.
 
The rating of the MCB for the lighting will depend on the cable size used. Typically they are 6A or 10A.

I wouldn't recommend putting both lighting circuits on on 6A MCB.

Could you change the 32A MCB for a 6A or is the circuit feeding other things?

Is the CU a dual RCD unit?
 
Well the obvious answer would be to take the downstairs lights 32amp MCB and put an appropiate one in it's stead
 
Hi Murdoch

The 32A is supplying another circuit.

The CU is an old type 4 way unit with push reset mcbs
 
Hi Murdoch

The 32A is supplying another circuit.

The CU is an old type 4 way unit with push reset mcbs

If the 32A MCB is supplying another circuit are you saying there are 2 or more cables into the MCB? Do you know what they other circuit is Could there be a FCU somewhere hidden that is the supply to the lighting circuit?
 
Hi Murdock,

No there are 3 cables going into the 32mcb. one which is 4mm and the other 2 are 1.5mm which one is the downstairs lighting circuit. I did not have time to check the other but i would presume it is the lighting circuit for the lights they have in the basement, maybe.


Could i change the 6A mcb to a 10A and put all the lighting circuits on the same one (providing calcs worked out)?
 
You should be able to asses what the 32 amp breaker is protecting. By the sizing off it you would expect to see a ring in there. Sounds as if there has been no room to add more circuits and someone has bodged this one. Needs a new board
 
Hum, I'm with Electricalserv. Sounds like an inspection would be the first step, then a new CU.

Certainly 2 x 1.5mm cables into a 32A MCB is not good, and changing it to a 6 or 10A without understanding what the 4mm cable is doing is asking for trouble.

Time to discuss your initial findings with the customer and gauge the best way forward.

It dosn't sound too safe as it is!
 
Hum, I'm with Electricalserv. Sounds like an inspection would be the first step, then a new CU.

Certainly 2 x 1.5mm cables into a 32A MCB is not good, and changing it to a 6 or 10A without understanding what the 4mm cable is doing is asking for trouble.

Time to discuss your initial findings with the customer and gauge the best way forward.

It dosn't sound too safe as it is!

4mm cable a radial and then 2 lighting circuits...sounds possible
 
Anything is possible, no point in spending too much time speculating.
 
Last edited by a moderator:
if space is tight, the best way forward is a RCBO board, to maximise the number of circuits in the smallest space.
 
3 circuits on one mcb is against the regs, 1.5mm (x 2) on a 32A mcb is against the regs if supplying more than one item. As above new board needed.
 
hi i think they are runninig a radial which would explain the 4 mm the two 1.5mms could be two lighting circuits i agree with the above def a cowboy way of doing it i think a new board would be the best idea but identify wat all the circuits do first though!!!! and you can print niceic stickers from the net so dont be fooled by that ask to see the installation cert if they evan have one.
 
Me thinks if I was on the spot with this I would check whats connected to the 32 amp breaker and as a safety issue move the 2 1.5mm to the other 6 amp breaker that way you are leaving it a whole lot safer than how you found it. plus check if there is any other 6 amp breakers as I have found a DB that had 3 1 for the downstairs lights, 1 for the burglar alarm and 1 for the front door bell the upstairs lighting was on a 16 amp with a socket so I doubled up the door bell and alarm to free a breaker.

Forgot to add NIECE or PIR complete stickers I treat this with contempt because I am sick and tired of following these guys after 3-6 months to find the very thing you are on about.
 