Hi guys, wondering if anyone's got suggestions for an intermittent fault.
Ground floor lighting circuit, Aprox 10 lights, mostly basic pendants occasionally trip 6A MCB.
Customer says it happens once every 2-3 weeks, no noticeable link to bad weather or time of day etc.
Also reports it happening when turning on different lights, but not always instantly and once they think It tripped with nothing switched on at all. So I assume a supply fault rather than a switch line fault?
MCB also protected by new RCD (tested and working fine) which has never tripped....so fault must be live to neutral....am I right?
When I arrive to test, neutral to CPC insulation resistance is around 2Mohms (no lights switched on) however within about 2 mins of being disconnected, rises back up to 150M ohm. How can the fault be between neutral and earth without tripping RCD?? Most of the lamps the customer has in are evil incandescent filament lamps- could there be equal leakage from live and neutral and this isn't detected by the RCD??
Any advice on how I can proceed with trying to separate the circuit to track down the culprit? I only seem to have a few minutes from disconnecting before the readings rise back up and the fault disappears.
Many thanks.
Ground floor lighting circuit, Aprox 10 lights, mostly basic pendants occasionally trip 6A MCB.
Customer says it happens once every 2-3 weeks, no noticeable link to bad weather or time of day etc.
Also reports it happening when turning on different lights, but not always instantly and once they think It tripped with nothing switched on at all. So I assume a supply fault rather than a switch line fault?
MCB also protected by new RCD (tested and working fine) which has never tripped....so fault must be live to neutral....am I right?
When I arrive to test, neutral to CPC insulation resistance is around 2Mohms (no lights switched on) however within about 2 mins of being disconnected, rises back up to 150M ohm. How can the fault be between neutral and earth without tripping RCD?? Most of the lamps the customer has in are evil incandescent filament lamps- could there be equal leakage from live and neutral and this isn't detected by the RCD??
Any advice on how I can proceed with trying to separate the circuit to track down the culprit? I only seem to have a few minutes from disconnecting before the readings rise back up and the fault disappears.
Many thanks.