L

llywelyn111

Hi,

We have installed some wall lights, the touch ones with three settings. We have a issue that they keep coming on randomly. Even when nobody is in the house they come on when they come home. It's on a TT system, could it be a appliance in a cycle? Small spike in voltage? or a ghost? The lights have been replaced once. Anyone come across this before?
 
and be sure to lock the doors and leave the lights on when you go to bed. wooooooooo
 
serves him right for fitting wall lights. these went out with the demise of gas lighting.
 
if you miss those days, try the amish community. they still won't use electrickery or automobiles
 
anyway, iv'e got the answer to the problem. it's ethernet. all those strange cyber waves in the atmosphere of the room switching the lights on.
 
Hi,

We have installed some wall lights, the touch ones with three settings. We have a issue that they keep coming on randomly. Even when nobody is in the house they come on when they come home. It's on a TT system, could it be a appliance in a cycle? Small spike in voltage? or a ghost? The lights have been replaced once. Anyone come across this before?

Firstly, You need to ensure that you have a good earth, so that the fitting can not pickup stray RFI signals.

As its a TT system, the ZS at the fitting will be in the region of 10-200 ohms, and not fraction of ohms.

The control electronics is being triggered by radiated RFI or conducted RFI.

If that's the case then the control electronics in the fittings are a bad design.

If the interference is conducted type then You will need to fit some type of HF filter,
in-line with the fitting supply, or convert to TN-C-S.

If its the radiated RFI, then you can not do much but to replace the fittings with a different make.
 
Last edited by a moderator:
I have a table lamp with inbuilt touch sensitive switching/dimmer. It comes on every time the computer is turned on and every time the scanner is used, they are in the same room. Earthing is good (PME). I have got used to turning it off, one two or three taps depending on how bright it is. I have always assumed it is transients much harder to get rid off than ghosts. One day I will get around to turning it off at the socket.

Why put off until tomorrow what you can put off 'till next week.
 
Touch switches that replace ordinary plate switches rarely use a neutral connection. As a consequence the electronics is often prone to false triggering by mains bourne transients or strong radiated RFI. There are a couple of things you can do to minimise this effect:- 1) Ensure the CPC is connected to the metal back-box. 2) Connect a mains rated CR (typically 0.1uF in series with 100Ω) snubber across the switch terminals. If the touch switch is currently mounted in a plastic cavity wall box, try changing the standard plastic box for the less common foil lined or metal type which has a CPC termination connected to the foil.
 
Last edited by a moderator:

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
lighting issue
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
26
Unsolved
--

Advert

Thread statistics

Created
llywelyn111,
Last reply from
MarkieSparkie,
Replies
26
Views
2,378

Advert

Back
Top