Thanks a lot really appreciated likeI’ve not traced everything but it mostly looks ok. The only thing that jumps out as odd is the fan isolator and light in the toilet.
Your drawing has the perm live in going through the fan isolator to the light switch common in series, and there is no perm live feed to the fan. That arrangement means the light can’t come on with the fan isolator off.
Instead put perm live in directly to COM of the light switch and either parallel from that to the perm live of the fan isolator or run a separate perm live from the JB to the fan isolator and on to the fan (for a timed fan). You can then have the light on with the fan isolator off.