after a few beers, that looks like a demented spider on LSD. i'll have another look in the morning.
 
And for your homework next week, we want the same configuration of lights and switches wired in;

a. 3 plate- loop in at light.

b. Neutral loop at switches.
 
and for the advanced course, use quinetic switches. but don't be touchy about it.
 
I’ve not traced everything but it mostly looks ok. The only thing that jumps out as odd is the fan isolator and light in the toilet.

Your drawing has the perm live in going through the fan isolator to the light switch common in series, and there is no perm live feed to the fan. That arrangement means the light can’t come on with the fan isolator off.

Instead put perm live in directly to COM of the light switch and either parallel from that to the perm live of the fan isolator or run a separate perm live from the JB to the fan isolator and on to the fan (for a timed fan). You can then have the light on with the fan isolator off.
 
I’ve not traced everything but it mostly looks ok. The only thing that jumps out as odd is the fan isolator and light in the toilet.

Your drawing has the perm live in going through the fan isolator to the light switch common in series, and there is no perm live feed to the fan. That arrangement means the light can’t come on with the fan isolator off.

Instead put perm live in directly to COM of the light switch and either parallel from that to the perm live of the fan isolator or run a separate perm live from the JB to the fan isolator and on to the fan (for a timed fan). You can then have the light on with the fan isolator off.
Thanks a lot really appreciated like
 
On a more general note, even if you have all the connections correct, a drawing like that with conductors snaking around the page is of little practical use because it is slow and error-prone to follow. Think about what it is trying to communicate; for example that room 2 switch is fed from the main permanent line terminal, then sends its switched line to the light via terminal 9, then the neutral goes back to the main neutral terminal. The line and neutral connections are more or less the same for every room, a fact that is not obvious at all from the drawing. The only unique thing about room 2 here is that its SL is on terminal 9, which can be shown without miles of spaghetti.

Investigate different ways of simplifying the drawing without losing any information. Research the difference between a schematic circuit diagram, which shows what is connected together without being specific about which terminals the wires go into, and a wiring diagram that physically details each cable and connector.
 

Reply to lighting joint box in the Lighting Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock