Live radiators fix ?

Discuss Live radiators fix ? in the UK Electrical Forum area at ElectriciansForums.net

J

Jak1708

Hi all

Got a customer in a few weeks time who has radiators that are live, isolated it to the downstairs ring, ive had it twice before in the past and just isolated parts of the circuit and then followed the cables until I found corroded cable on a pipe which when replaced fixed it.

As I say this worked fine both times and it's what I'll do this time again but just wondered if anyone else had had this same fault and if you got round it in a different / better way ?

Thanks

J
 
Could be a faulty RCD.

That needs sorting ASAP, with RCD etc checked. Some people are just idiots, if it was a leaking radiator it would be sorted tonight. A leaking radiator shouldn't kill anyone, a live one might.
 
I've had a live gas pipe before but there was no other copper in the house at the time. Tracked the offending item down and repaired it, funnily enough it was a pipe monkey who found that too
 
I've only had calls for "shocks" off metal work that has turned out to be nothing more than static.

Don't think I'd fancy a job like this one where the radiators and probably a lot of other pipework is live, but customer doesn't seem to want to sort it. I'd start to look at covering my backside and getting something in writing recommending immediate remedial action.
 
I've had live pipework before, but only on TT systems where the (usually very old) rod has rotted out and so no effective path to earth to trip mcbs. And usually a voelcb that doesn't work. I usually get converted to TN-C-S and go from there.

Like above, I'd get something in writing - issue a danger notice using signed for delivery (and email a copy if you can).
 
Cool cheers for the input guys.

I imagine all this live copper was along the same Lines as nail through the cable and touching copper or bare conducter badley terminated etc ?

I don't think they quite realise the size of a radiator system could be anywhere :S
 
Last edited by a moderator:
5773dd89-5253-eef2.jpg


Found this in what was going to be newly refurbished nursery my uncle who is a plumber got me in to have a look as he kept getting belts. Luckily it happened to him and not one of the children. Another case of builder who can 'do' electrics.
 
I would be looking for three things immediately;

1 Localise and repair the low insulation fault causing the leakage current.
2 Why is the touch voltage so high? Where's the bonding and why isn't it working?
3 Why isn't the RCD tripping and isolating the supply to the faulty circuit?
 
Ive had live rads intermittent on a job, ... now i posted this before but i let you try work this one out.... to note the dno fuse was withdrawn by the clark of electrical works and they still came live roughly dinner times and tea time, i worked it out and was laughed at by clrk of works until he was smuggly proven wrong by me :)
Just to add it was a tns with corroded armoured which gave bad earth so it was converted to tt with earth rods.
 
Last edited:
Similar in that it was external as you might have guessed, turned out it was a faulty microwave 2 doors up, and throughout the street the old wooden box buried DNO joints had corroded along with the earthing of the SWA, when i earth rodded the house i was in i effectively gave a better return path to the house up the street than its corroded supply cable acheived. Was a real head scratcher to solve as plumber complained he had shocks but whenever we tested the microwave wasnt on, we withdrew DNO fuse and let the plumber continue and you guessed it ZAPPP!, i suggested to clark of works what it was to which he said he'd been doing his job 35yrs and never heard of anything like that and said i was clutching at straws... i said so just cos you haven't heard of this issue your willing to cast it aside and have a installation with a potentially lethal senerio, i said il contact the DNO then and get them out. They confirmed everything i said although my guess was an electric cooker they confirmed it to be a microwave and id created an alternative earth path.... and like your set-up Tony -- all street powered down, road dug and all houses new supply cable, and me 2 earth rods back that had be billed. Although it didnt make up for the time lost on fault.
 

Reply to Live radiators fix ? in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock