Firstly - apologies if this is in the wrong place but I couldn't seem to post in the DIY area.

I have removed a socket cover in order to decorate and replaced it to find it didn't work. This socket is in a bedroom on a separate ring to the main sockets, with just the two bedrooms sockets on it.

Using a voltmeter I have measured the live - neutral which is 0V, (not right), and the live to earth (240V).
So I also checked the neutral to earth which was also 0V.

I wasn't sure if the live had shorted to the neutral so checked the resistance between the two with a multimeter, this was greater than 2MOhm (limit of my multimeter).

Anything obvious that I am missing before I call in a professional, I understand the theory well as its part of my job but I don't do any electrical installation.
 
Please JW get an electrician in. You have gone too far as it is. Leave it to us, post up your location and get it sorted out.
 
Last edited by a moderator:
Anything obvious that I am missing before I call in a professional, I understand the theory well as its part of my job but I don't do any electrical installation.

Yes, it is obvious what you are missing and if you did understand the theory you would deduce it from the test results you have. As already said, genuinely, get an electrician in to effect the repair required on that circuit and then confirm by testing (with equipment you won't have) that it safe for continued use.
 
Wow, surprised at the arrogance of electricians when they have no idea about other professions who design electrical systems. I have found and fixed the problem, which was quite obvious in the end, I was using a cheap DVM from toolstation which obviously has a very low internal bleed resistance and allowed the neutral wire to charge up which had come loose from another plug. But again thanks for the incredibly helpful responses.
 
Wow, surprised at the arrogance of electricians when they have no idea about other professions who design electrical systems. I have found and fixed the problem, which was quite obvious in the end, I was using a cheap DVM from toolstation which obviously has a very low internal bleed resistance and allowed the neutral wire to charge up which had come loose from another plug. But again thanks for the incredibly helpful responses.

I don't think it was arrogance, I think it was sensible advice. Would you let a milkman fix your car?
 
wouldn't it be better if the forum gave a automated "Get an electrician in" text on certain questions or a header note stating that only expert electricians will be helped (kind of an oxymoron really though)
 
wouldn't it be better if the forum gave a automated "Get an electrician in" text on certain questions or a header note stating that only expert electricians will be helped (kind of an oxymoron really though)
That's not really relevant in this instance is it? There are guys who obviously have a good deal of experience and just need a bit of advice, and there there is "allowed the neutral wire to charge up which had come loose from another plug", which should have the automated "get a sparky in" response......
 
Wow, surprised at the arrogance of electricians when they have no idea about other professions who design electrical systems. I have found and fixed the problem, which was quite obvious in the end, I was using a cheap DVM from toolstation which obviously has a very low internal bleed resistance and allowed the neutral wire to charge up which had come loose from another plug. But again thanks for the incredibly helpful responses.

One could put postulate that if you knew more than your original post suggested then you'd not be calling it a plug :)

Sorry if you feel offended but the forum is littered with DIYers wanting free help which is neither safe or viable to do in a forum environment.

Your post suggests you are an electrical designer? I have a large commercial new build coming up - any chance you could design the electrical installation for me, for free? :) (obviously I'm being flippant).
 
Wow, surprised at the arrogance of electricians when they have no idea about other professions who design electrical systems. I have found and fixed the problem, which was quite obvious in the end, I was using a cheap DVM from toolstation which obviously has a very low internal bleed resistance and allowed the neutral wire to charge up which had come loose from another plug. But again thanks for the incredibly helpful responses.

Awww come on, I haven't even had a chance to join in on this one yet!

But Anyways, I'm not sure I follow how you think the neutral has charged up and what effect it had on your test results? The potential readings you stated suggest a disconnected/broken/missing ( or whatever you want to call it) neutral.

A word of advise, cheap meters are very unlikely to meet the appropriate safety standards for use on live mains, it could be very dangerous for you as the user. Better to use a good quality meter


Sent from my iPad using Tapatalk
 
what he could mean is that if the N is broken/open circuit between the point where he's testing and the N of the supply, then his N could be sitting at 240V via a load upstream.i.e no current flow L-N, hence no VD. so he'll read 0V L-N.
 
wouldn't it be better if the forum gave a automated "Get an electrician in" text on certain questions or a header note stating that only expert electricians will be helped (kind of an oxymoron really though)
Wow, surprised at the arrogance of electricians when they have no idea about other professions who design electrical systems. I have found and fixed the problem, which was quite obvious in the end, I was using a cheap DVM from toolstation which obviously has a very low internal bleed resistance and allowed the neutral wire to charge up which had come loose from another plug. But again thanks for the incredibly helpful responses.
It's quite incredible how you people expect complete strangers to give up their free time to help when you have this kind of attitude.
It's not just you but it seems to be that everyone who sits in an office doing drawings assumes they can extrapolate that into the real world simply because their drawings are related to electrical systems, and that the manual element is in some way beneath them.
Remember who is asking for whose help here.
 
Wow, surprised at the arrogance of electricians when they have no idea about other professions who design electrical systems. I have found and fixed the problem, which was quite obvious in the end, I was using a cheap DVM from toolstation which obviously has a very low internal bleed resistance and allowed the neutral wire to charge up which had come loose from another plug. But again thanks for the incredibly helpful responses.
just remember that both the titanic and the hindenburg were "designed".
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Live to Neutral voltage issue at socket
Prefix
Forum
UK Electrical Forum
Start date
Last reply date
Replies
15
Unsolved
--

Advert

Thread statistics

Created
jw4774,
Last reply from
Lucien Nunes,
Replies
15
Views
4,658

Advert

Back
Top