Ip 65 rated boiler sat on concrete slab next to building.flow and return pipe leaving boiler,entering building without contact with soil.main bonding or not ?
 
yes best option.but if board on other side of building perhaps a costly one.real question i suppose are the pipes extraneous since not connected to soil,bit puzzling really
 
dont think connected to soil is anything to do with extraneous. extraneous is something that can introduce earth potential but is not part of the electrical installation.
 
yeah osg p.27 metal central heating and air conditioning systems require equipotential bonding

Only if they are extraneous conductive parts.....Generally an AC or CH system is wholly within the equipotential zone and so is not classed as an extraneous conductive part and therefore will not require main bonding.
If the boiler is external,in contact with the ground, with metallic pipework coming into the building it is likely that the pipes will be extraneous conductive and will require main bonding at the point of entry.
 
can,t produce an earth potential if its not connected to the earth[soil] can it whatever it is
 
dont think connected to soil is anything to do with extraneous. extraneous is something that can introduce earth potential but is not part of the electrical installation.

and if these pipes are not connected to the soil how would they introduce an earth potential?
 
are you confusing main bonding with supplementry bonding no need to cross bond boiler pipes anymore.are,nt flow and return just boiler pipes?
 
no supp bonding required if installation meets 7671, personally if there is exposed metal pipe work outside i would bond it and have done with the worry.is it a big hassle to do now?
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
main bonding to external boilers
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
27

Advert

Thread statistics

Created
nick611,
Last reply from
Deleted member 9648,
Replies
27
Views
4,900

Advert

Back
Top