Hello first time here site looks good. Need to install main bonding at a school, gas and water aprox 80m away from dis board. Wanted to check size of cable to use. Do i need to increase size from 10mm.
 
What do the regs say ? I have not checked but I think you will find it says that once the neutral conductor is up to 35mm csa then the earthing conductor must be equal to the neutral. therefore main equipotential bonding conductors must be half the csa of the main bonding conductor or the next nearest size csa up from that. So, if you have a 50mm neutral conductor you would have a 50mm earthing conductor and therefore a 25mm main equipotential bonding conductor.

Do check the regs though.

Regards

SC
 

Reply to Main Bonding in the Commercial Electrical Advice area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock