Deleted member 26818
Nah, just guess it.I was thinking to compare this Ze with line to neutral impedance.
Discuss Main Earthing Conductor and Earthing System question. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
PME conditions can apply to TN-S.
PME (Protective Multiple Earthing) is used where a network is configured as TN-C (earth and Neutral combined).Please explain what ypu mean by “PME conditions”?
It’s primary purpose is to keep the difference in potential between the combined earth and neutral and the general mass of the earth as close to zero as possible.
One of the ‘conditions’ associated with PME systems is that neutral current from other installations will be present on earthing and bonding conductors in a particular installation.
Hence the requirement for larger CSA bonding conductors.
Older networks configured as TN-S are being changed to TN-C.
Whilst installations may be presented with TN-S, the bulk of the network is TN-C with PME.
When conducting a periodic inspection on an installation which is presented as TN-S, the Inspector should determine whether PME conditions apply and whether the CSA of bonding conductors is adequate.
One method to determine this is to measure the Ze.
A Ze close to or below the typical value for a TN-C-S system would suggest PME conditions apply.
A further test would be to compare the values for PSSC and PEFC.
Not sure whether I should be flattered or insulted, that you believe my post is copied and pasted?This is a great copy and paste describing why a TNC-S is not always a PME.
It still does not explain how a TN-S can have ‘PME conditions’.
When taken into consideration with the fact that you deliberately misconstrue it’s intent, I can only assume it’s a puerile attempt at insulting me.
In any event, I have attempted to educate and inform you, as per your request.
I suggest you either take it on board, or remain in blissful ignorance.
Almost every time an underground joint is made it is earthed, often by just burying bare conductor but sometimes by a rod with (often bare) conductor crimped to it. A tns supply that has had multiple joints will have multiple earthing points so you can be presented with a supply that looks like tns but has Protective Multiple Earthing along it's route
Sorry son doesn't know on a tns, yes on tncs. He works more on the hv distribution sideWould those joint earths be linked to the neutral?
Reply to Main Earthing Conductor and Earthing System question. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net